Is that for real?
Look at all the bare live copper showing.
Yep unfortunately it is. It’s part of the light circuit!!
So far I have:
6 x C1’s including the one posted.
13 x C2’s
2 x FI’s
I’ve still got a fair way to go but safe to say the landlord is not happy with the previous inspection. ?
So far I have:
13 x C2’s
2 x FI’s
The letting agency need to be aware of this. I would point out to them that whoever is doing their EICRs is blatantly leaving them open to future court cases.
So far I have:
13 x C2’s
2 x FI’s
Must have been one of those new 'drive by' inspections that I keep reading about...
They have already given them a ‘don’t call us we‘ll call you!’ They had their concerns hence asking me to give a second opinion. When I saw the consumer unit was fed direct from the meter via 16mm T&E and it was on a 100A cutout I knew things weren’t going to go well. I phoned the estate agent at that point and said I had only opened the meter cabinet and already graded it unsatisfactory as 16mm T&E is rated at 85A at best. It may well have a 80A fuse inside the cutout. But as I cant pull it to check then I have to go by what it says on the carrier. I calculated the max demand using diversity to be 86.8A so I doubt it’s on a 80a fuse.
Plus it’s a TN-C-S system and the main earth is the 6mm CPC from the 16mm T&E, that and there are exposed single insulated cores going into to the meter.
I guess the last inspection was by ‘Bodgeit & Scarper’ ?
Could well be an 80A fuse - the house won't draw anywhere near that figure.
I know. But my experience round here is that if it says 100A it generally is. They usually stick a label on to say 80A.
It’s possible but I can’t confirm without the DNO pulling it for me.
Is it sealed?
If not, says it all.
If so, they've sealed the meter with a 16mm T+E outgoer......is that right?
Joke all round.
Out of interest, are Bodgeit & Scarper a member of any of the scams ? If so then 2 things come to mind :
1) It's proof (not that any more was needed) that scam membership is no guarantee of even safe work - let alone good and standards compliant work.
2) It needs reporting and see what happens. My w.a.g. on that would be "s.f.a." ?
So whoever fitted the meter is the one who connected the source end of the 16mm2 T&E?? Word fail me!
Incidentally, I used to do the odd new build for a local building firm, and when they paid me, the cheques were genuinely in the name of Bodgeit & Scarper.
It would appear so. Although I’m not overly convinced this has been done by the DNO.
Then again this is the state of the service cables. ??‍♂️
Service cable looks like the work of whoever fitted the uPVC soffit and barge boards.
If the meter has the correct seal on it and it hasn't been tampered with, then it must have been the meter installer, unless the T&E is wedged in with matchsticks.
There is an entire housing estate near me (I think built around 1985/1990 ish) wired in exactly the same way as the above picture, 10mm twin and earth connected to the meter which then snakes up through the cavity to the consumer unit. I have worked on dozens of these houses and all are wired in twin n earth from the meter to the board. So can only assume this was the original design and connected by the DNO like this