As the title says, does a three-pin socket (external) used as charging point need an earth electrode or open PEN fault? Are mode 1 and mode 2 exempt from this ?

I was under the impression that anything used as EV charging point and if located externally, the installation would need to have either TT or open PEN fault detection device, if the supply to the site/building is TN-C-S.

The charger will draw max of 12amps.

Thanks.

Regards,
J
 
Last edited:
No, as far as the regs are concerned it's just a standard outlet (requiring rcd etc).

However I think 'granny chargers' should be prohibited as they don't properly provide the protection normally afforded by a normal charge point, and they run at 100% load permanently - not really the sort of load expected on a 13A socket outlet.

So it would be good practice to add it, but the danger is the outlet may be used for 'normal' loads which would be better on tcns
 
I'm following this thread as I recently raised a very similar question, and no one bit, for probably understandable reasons as it's a horrible question!
In my case it was a 16A socket though.

I asked :
My more philosophical question is if you take a plain and simple 16A socket and decide to plug an EV into it does it, or does it not become mode 1 charging under section 722, and the delightful 722.411.4.1 then applies?
1626717243617.png

Or is that just too far fetched?"
 
The problem is the term charging point, a standard socket isn't this, the charging point is actually the 'granny charger' itself or a proper charge point (they are not chargers, the actual charger is in the car).

As for any point that could reasonably be used....

That could imply that pretty much every outside capable supply, such as near the front door etc needs the extra protection, and that really is unreasonable
 
My pragmatic conclusion was that if asked to fit an EV charging point, you fit an EV charging point.
If asked to fit a 13a or 16a socket, you fit a socket. Unless told at the outset it's for EV charging what more can you do?
In my case I was asked for a 16A socket for a welder which I provided. The parting shot was "It's great, I can use that for my car too". I decided not to hear that and ran!
 
Thanks for the replies guys.

So even if the socket is labelled charging point, it won't require additional protections.
It isn't a charging point, look at the definition in section 722 a charging point is the part which plugs into the car you do not plug the car directly into a 13A socket outlet, you connect the socket outlet to a charging point, then this connects to the car.
 
It isn't a charging point, look at the definition in section 722 a charging point is the part which plugs into the car you do not plug the car directly into a 13A socket outlet, you connect the socket outlet to a charging point, then this connects to the car.
Being honest I find this confusing (amendment one):
1627382592801.png
 
But, happy days, it doesn't matter. Just noticed mode 1 charging says:

1627382876794.png

Note "utilizing the power and protective earth conductors"
Isn't that the answer, for up to 16A?

(Edit, but the catch-all PEN conductor ban in 722.312.2.1 still applies of course unless one of the idents of 722.411.4.1 is used. )
 
Last edited:
Add in Rolec's EVWP0020 to add a bit more confusion to the mix.
Isn't that one just a glorified socket and RCBO?
I think that's an easy one, definitely an EV charging point, no built in OpenPen protection as far as I can see, so options are
1 - TT it
2 - PME + extra earthing as per indent ii) to achieve 70v touch voltage
3 - PME, and add separate upstream OpenPen protection to comply with indent iv)

(or just use a decent charging point in the first place!)
 
Should be genuine TNS added to the list above.
Agreed - I seem to recall you saying you can actually see yours in genuine, which is a lovely luxury...

My conclusion for now is that as @Julie points out it's really undesirable to be regularly charging an EV with a 13A socket in the first place, so the confusion (at least on my part) on how the regs apply to the worst way to charge an EV is pretty academic.
 
Agreed - I seem to recall you saying you can actually see yours in genuine, which is a lovely luxury...

My conclusion for now is that as @Julie points out it's really undesirable to be regularly charging an EV with a 13A socket in the first place, so the confusion (at least on my part) on how the regs apply to the worst way to charge an EV is pretty academic.
Yes, it is but there are little buggies which charge from standard socket. Hopefully, they phase out the socket chargers and standardise the type 2. They are mainly for carrying stuff in short distances but still classed as an EV.
 
It is slightly bizarre as the risk from a EV charger relating to use with a PEN is nothing to do with the charging, it is the big lump of metal on the CPC that someone might be washing outside. Dedicated high-rate charger or 13A plug I'm not sure there is a difference here.

But...is there? Do cars charging from a 13A/16A outlets actually use double-insulated (class II) systems so the PEN-connected-CPC is irrelevant?
 
It is slightly bizarre as the risk from a EV charger relating to use with a PEN is nothing to do with the charging, it is the big lump of metal on the CPC that someone might be washing outside. Dedicated high-rate charger or 13A plug I'm not sure there is a difference here.

But...is there? Do cars charging from a 13A/16A outlets actually use double-insulated (class II) systems so the PEN-connected-CPC is irrelevant?
I don't think so, they provide 230v to the car itself, so there is no guarantee that is class ii
 
No, as far as the regs are concerned it's just a standard outlet (requiring rcd etc).

However I think 'granny chargers' should be prohibited as they don't properly provide the protection normally afforded by a normal charge point, and they run at 100% load permanently - not really the sort of load expected on a 13A socket outlet.

So it would be good practice to add it, but the danger is the outlet may be used for 'normal' loads which would be better on tcns
Agree with Julie. Worth pointing out that i see a lot of burned out sockets as they just cant handle a prolonged load for several hours
 

Reply to Does a three-pin socket used for Electrical Vehicle charging need a earth electrode or open PEN fault detection device? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I understand the requirement for PEN fault detection on EV chargers for TN-C-S installs (or to place an earth rod). However, when I was...
Replies
3
Views
1K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Just looking for a bit more information on Mode 2 charging of electric vehicles. The mode 2 charging cables state they have protection against...
Replies
4
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
786
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock