Aaron b

Mentor
Esteemed
Arms
Reaction score
334
Hello, I have recently designed a system including a pump. It is only 4amp and it is controlled using a crompton DOL. An external twist to reset estop has been incorporated in the circuit in series with the stop button. The client has requested the addition timer to autorun the pump daily.

I don't want the pump to be started automatically and bypass the estop and want it as simple as possible. I can add a 2 pole relay and a estop reset button and break the line conductor to the push buttons but I was wondering if there was a simpler way that I may have overlooked?

efT2s-8P0QB73he5WZo_d-4fE5pj_Q1fZtLVL1jrpT4BMJ_lwLSk2GCMF5snBFiRgnF_PwGizcfVfpnZLevYykb1Z1InxXnLsLwC_YFWMEHZNN6r1w1QlNSTmabTPD9Kh__cZ_uYyLQ8Vp16K0MqsRMQEprL73AhJAg8y2i_FR2ZwKTkXwKHsYVxNIm_8Bx4T8flY1q305ZergVwsp0UVUWo53w3PD5knPbtjL5OeZ2MJQnTJggcOW2fOyiRgJ5uCTT6D_YUXWVBXX14FZL1bOmEFPImb8v2pZxGockPjSOakbghB5CZvikhCnyly8aj_OTJ86NyLceL73lvwkKUgsi0h_i1gNplW7SAUIrAdllQuOhm3y43CdcQRd6XP6I8SrXGFhWHCTJALgFZQsq3yQkl3T1iXdKYQCI5Wzwu2g9yE5zDaueDzP5jEvJWhV0CTJnkUb4_mtk0OmrVkMIChvvCffPlYArVE_9_oUG5Nz3xtyRG4OTrghDK7uCSSyph5XvdkV92cQ3WvfG_A1wRBhnrqJWiiXLWSIkf1GZhkVfQ4TX_U4adCI89Vt0uUFHtBoo7bFtfWbgRTALiFO1gWhQ2aO6GucVZm0w4GnQkff6TuZ7X7TWauPnjNzBMcI-RdKa6kU4CKPl6drUXTkIm62ypzgw7mF93K8LHyNsL3cA6RAh2fEyoIz7id1n_pi4Uw6E_p8IYIe0PZCr_8XW5aRe2VA=w1673-h942-no
 
I missed that I would need to have a normally closed contact from the timer too, to stop the aux contact on the contactor latching.
 
Post this on the trainee forum. Is this really for a client or for a college question?
Thanks, it's a real job. I joined the trainee section of the forum as I never completed my apprenticeship so I am going back through the experienced worker route. I don't have any experienced peers so I was just wondering if it was anything others have come across and if there was another method I might have overlooked.
 
Do you require E-stops or just stop buttons?
If E-stops then you need to do a risk assessment to determine what category of stop you need.
Also when designing things like this, it have to comply with EN60204 along with other regs.
 
Do you require E-stops or just stop buttons?
If E-stops then you need to do a risk assessment to determine what category of stop you need.
Also when designing things like this, it have to comply with EN60204 along with other regs.

The client requested a separate estop and their engineering specifications require that its in an enclosure with a isolator. Personally I think it should have been waivered as the stop button is raised on the starter. I have enough room to add some components in that enclosure now but will have to replace the front as I haven't laid it out for a reset button. Thanks for the prompt, it's a fully enclosed pump with no accessable rotating parts so the risk is minimal but I'll have another look at the standards as it's been a while.
 

Reply to DOL with external e-stop and auto-start timer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all I would like a bit of advice to do with a DOL starter ill be fitting. Basically I'm replacing an old water damaged crabtree DOL starter...
Replies
8
Views
2K
I previously posted about having a single phase reversing motor which I thought had a centrifugal switch. After looking into it more, it actually...
Replies
1
Views
1K
Hello. I bought an old three phase compressor but it has come without a starter switch. Just five cables, two for the pressure switch and three...
Replies
9
Views
5K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
I recently moved into a new flat that is fitted with a horstmann E7 water heater. The tank has 2 elements connected, one at the bottom of the...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock