Hi, I don't know if anyone can help with this. A customer called me out saying that a British Gas boiler service had highlighted a socket showing >2000 on the EFLI test. I went to look and got 1.12 on one side of the (two gang) socket and >2000 on the other. I assumed it was a dodgy socket and replaced it.

Testing the replacement I'm now getting about 1.15 as a loop test when the socket's off the wall but >2000 once I screw it in. I can't find any voltage on the back box.

Any ideas please?
 
Somehow earth continuity is breaking down. What do you mean by can't find voltage on the back box.
 
All I can think of is a dodgy connection on the different test lead or plug adaptor thingy. So you are getting decent-ish reading on the conductors, but a crap reading through a new socket, so have assumed you are using an additional test adaptor or a change of leads to do that test.
 
The initial fault sounds strange as it is difficult to disconnect the earthing from one side of socket but I suppose it is possible, it is more likely (but still unlikely) to have been a damaged earth connector at the socket, e.g. pushed to one side by the plug pin.

Once the socket front has been replaced I woudl assume that there is a poor connection to the earth terminal, perhaps the sleeving is caught on the screw, such that when the conductors are moved as the socket is screwed back the earth disconnects. This would be much more likely if both cpcs are in the same terminal or there is an earth discontinuity on one leg of the ring.
 
Sounds like the first socket must have been faulty. But the change as the socket is screwed in must be a break in the CPC (s) surely?
 
Are you using plug method and on L-PE? and as others said is it a ring circuit? And what was the gas man doing a loop test for ????
 
Last edited by a moderator:
Are you using plug method and on L-PE? and as others said is it a ring circuit? And what was the gas man doing a loop test for ????
B.G did this with socket tester when they came to service our boiler asked why he said to prove boiler had earth (boiler on own circuit radial)
 
This whole thing dont make sense. If the boiler is on own radial then it has a spur yes? Where does the socket come into it? But anyway clearly the earth makes and breaks when the wires are in different position. And anyway a socket tester will not give you an ohmic measurement. Confused I am.
 
The socket tester that BG used was probably one of those that give a very rough idea of efli: there is one that has measurements something like <1; <5; >5 ohms. So when BG 'measure' it, there is no leeway for TT earthing.

To the OP, is the socket on a stud wall with a socket on the other side of the wall perhaps. The act of screwing back the face plate could be pushing the cable/conductors at an adjacent socket out of position.

Also test the R1 value with the face plate back, as it could be that and not the R2 causing the issue. Although I would suspect the CPC to be the cause.
 
He could also have a social life unlike us sad sacks.:confused:
 
Tis a bit rude to ask for advice and not reply. I had to cook the tea last night, but can still find a spare moment. :rolleyes:
you cooked last night and still able to post today. i admire that.
 

Reply to Domestic socket loop test puzzle. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
967
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
  • Locked
After completing a new RFC or modifying an existing one, I will always test continuity across all 3 conductors at the Consumer unit. I use the...
Replies
48
Views
6K
hi there as i write this i realise i have 3 interconnected questions about fused switches; two relating to my boiler (hope its not to cheeky to...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock