R

Robo

In my opinion this applies to fixtures and fittings. I had this conversation with somebody else and they ink it also refers to SWA and armoured cables?
 
I'm to so sure mate, I got some print outs to help with the schedule of inspections and it refers to Double insulated fittings. ( has the the square inside a square printed on it). And nothing about cables.?
 
I don't think it refers to cables either, i take that definition as meaning enclosures, containment's, fittings and the like... More than happy to be corrected though!! lol!!
 
Defo not the cables it's enclosures, accessories etc.
 
It applies to any accessories or enclosure that has the double square on for the double insulation. The reinforced insulation is usually any specialised site applied insulation and would only normally be found in specialised installations for a specific purpose. When I was taught at college many moons ago the instructor who was a senior examiner previously at C&G said he had only ever done reinforced insulation once in a coal mine!
 
As much of the other posts. Double insulation applies to class 2 fittings and enclosures, and reinforced is specialist stuff.
Dont confuse this with the Pat stuff, where double and/or reinforced insulation in class 2 appliances provides both basic and fault protection by its construction.

Cheers............Howard.
 
Double and reinforced insulation cannot apply to cable. What many refer to as "double insulated" cable is in fact insulated and sheathed cable.

Protection by double or reinforced insulation refers to that being the protective measure for the installation/part of an installation, and therefore will not apply if the installation is protected by ADS (regardless of whether or not it contains equipment which is of a Class II construction).

Essentially, except in very specialist circumstances, it will always be recorded as "N/A" on the schedule of inspections.
 
Double and reinforced insulation cannot apply to cable. What many refer to as "double insulated" cable is in fact insulated and sheathed cable.

Protection by double or reinforced insulation refers to that being the protective measure for the installation/part of an installation, and therefore will not apply if the installation is protected by ADS (regardless of whether or not it contains equipment which is of a Class II construction).

Essentially, except in very specialist circumstances, it will always be recorded as "N/A" on the schedule of inspections.

Couldn't have put it better :)
 

Reply to Double and reinforced insulation. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
795
Opinions on this Crabtree TP 10 way board? Got to test this next week after a quick recce on a clients site yesterday. Although probably...
Replies
12
Views
1K
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
479
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K
Hi, Just interested in learning what others do when faced with an old lighting installation where there is no earth and you’re installing a metal...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock