Hi,

As you may guess from the post title, I need to add a second socket. It is in an outhouse, built onto the main building. There is currently a single socket in the outhouse, which is spurred off the first-floor mains ring.

I believe the regs say any additional socket must be daisy-chained from the existing one. However, as the mains feed enters into the outbuilding, it passes through a 30A junction box, which doesn't do anything at all (i.e. one wire in, one wire out). This junction box is in the perfect location to take the second socket where it needs to go, but I am guessing the junction box is treated no differently to a socket, and so I am not allowed simply to put another wire into there to go to the second socket?

I'll try to clarify all of this:

I currently have this: RING-MAIN---30A-JB---SOCKET1

I am assuming I must do this: RING-MAIN---30A-JB--SOCKET1---SOCKET2

I am assuming I cannot do this:
RING-MAIN---30A-JB--->
-->SOCKET1
-->SOCKET2
|
(The diagram maybe more confusing than the words. I can't figure out how to get decent formatting for this second option without attaching an image.)

Kind wishes - Patrick
 
Unfortunately, you can’t do either of them.
If you want to add a radial circuit to a ring, it can only have 1 socket on it unless it is fused down using an fcu or similar.
 
You need to put a fused connection unit at that junction box before the socket in the outbuilding. You can then have a second socket but will of course be limited by the 13 amp fuse in the fused connection unit.
Make sure you got rcd protection. If you haven't then swap the junction box for a small metal enclosure and put an rcd in it.

Thank you so much! That has saved me a boat-load of work, not to mention double the wiring (bad for the planet and generally bad anyway). That solution hadn't occurred to me.

The circuit is already RCD protected, so I'm fine there.

Kind wishes - Patrick
 

Reply to Double-check on wiring regs for adding socket in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock