Discuss Double Trouble in the The Welcome Forum area at ElectriciansForums.net
EddieB
Whilst replacing an old DB I found that an outside light had been wired in and doubled up at the MCB, foolishly I had counted the the old fuses without taking the cover off, the new DB I had bought allowed for no more expansion can I double up at the MCB with this extra light, rings circuits I know is a no goer for an additional socket to be added due to the rating of the MCB (32a) but can I double up on a lighting circuit.:confused:
Welcome!
What happens if the customer wants additional installs in the future and no spare ways?
Not good practice to double up and it doesn't comply, I would just exchange the CU for one with more ways plus expansion.
Warren G
Thanks for the prompt reply Let's assume I cannot change it, I know it aint good practise but what doesn't it comply to? is there a regulation that stipulates you cannot do it.
Hi mate,
Take a look at Big Red - 314 Division of Installation (314.4) in particular.
Sorry Mr G gotta disagree with ya there!
Doubling up on an MCB is no different from teeing off of a rose somewhere!
As long as ALL the lighting is not on one MCB if there are just 2 circuits then no prob!
Same with RFC and spurring off 32A MCB. No Different than a spur from a socket outlet.
Very logical point Jas, think your right on that! :eek:
Had a dig around and found thats its a question / answer that is published in the NICEIC technical helpline book 'From the phoneline'....
Question There are no spare ways in the DB for my new lighting circuit can i use a existing one?
Answer YES although Reg 314.4 requires each final circuit to be connected to a seperate way in a bistribution board, a circuit may have more than one "branch" connected to the appropriate way.
nice one! ;)
Thanks boys
It's good to Talk
There you go mate, thanks what the forums all about. A logical answer. ;)
Reply to Double Trouble in the The Welcome Forum area at ElectriciansForums.net