Ducksy

Hey guys I see this now and again on my rounds....8.5kw method C on 2 x 2.5mm cable......does it state anywhere in the regs that it a radial must be a single cable Or is it acceptable ? the very least i think its lazy not using 6mm but as always I'm well off from the more experienced guys think ;)

Thanks

 
and the cables must take the same route. if protected with a 40A MCB, the cables should not be overloaded, method C, but , not good practice, IMO.
 
What happens when the shower is replaced with a 500kW unit? Kablammo. height of laziness! who be arsed pulling in and clipping 2x2.5mm² cables when 1 x 6mm² would have been handier, easier, safer etc.
 
What happens when the shower is replaced with a 500kW unit? Kablammo. height of laziness! who be arsed pulling in and clipping 2x2.5mm² cables when 1 x 6mm² would have been handier, easier, safer etc.

Going to need, probably, at least 2x6mm I think......or it's own power station :lol:
 
How would you work out the current carrying capacity of this set up? If its a ring then the maximum overcurrent device allowed is 32a, but this is 5mm??!?!?! where is this cable in BS7671.

Also what happens when one of the phase or neutrals comes out?

i wouldnt be thinking this is an acceptable way of doing things but hey this is why this forum is here!
 
Sounds like a guess. If its not in BS7671 and you can tget information from the manufacturer then you will be guessing.

Although 2.5mm is rated around 27A (clipped direct and depending on its run), the ring will not necessarily put equal load on each cable and hence the 32A device. In your case the cables may well be the same length and therefore in theory should split the load equally. But this does not take into account resistance at the terminations. again this is an unknown. in the event that one side comes free, a 32A MCB will be just enough to protect the cable. In your sitaution it will not be and you will have a fire.

You cant back yourself up in a court case with guesswork. If you go by BS7671 then you will not have unknowns and you will not be guessing. No one will be able to argue.
 
how about just treating that radial as a ring, with single accessory connected at the end of it?
if its sits on its own 32a breaker should be up to the regs?
 
unorthodox but no problem at all using 2 feeds to a fixed equipment so long as they're the same length ( for load balancing reasons ) and both cables are wired into the same terminals at the CU ( for identification purposes )
 

Reply to doubled cable on a radial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
615
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hey guys , went to a job last night to quote for a new shower install ... After removing the old shower front , I discovered 2 X 2.5mm t&e instead...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock