I'm testing a car park lighting circuit at 200m long. 4mm singles to first point at about 100m and then reduces down to 2.5mm. Trunking used as additional CPC to reduce Zs values. How would you record that on a test sheet? And is there a regulation about downsizing?
 
I wouldn't see a problem with downsizing cabling as long as Zs is okay and the OCPD is suitably sized for the smallest cable CSA.
 
Ok. But on the test sheet will I put it as a 2.5mm circuit on schedule of test results, and then put in a deviation explaining 4mm to first point for design section to sign.
 
Go for your worst case and record it as 2.5mm for the circuit. If its compliant overall then there is no issue with this.

In any remarks column (or notes sheet) record the downsizing of the cable so its obvious on any future inspections what has happened within the design of the system.
 

Reply to down sizing long lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
854
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock