magnoliafan89

-
Esteemed
Arms
Reaction score
540
Hi guys

I was doing a kitchen recently and behind the cooker hood I had ran 2.5mm from a FCU, the hood can with 1.5mm flex. I had put a plug top with a 3amp fuse onto the flex and then a single socket for the 2.5. That way you just plug it in.
The kitchen fitter got all assy and said that his normal electrician normally just shoves a junction box up there and it looked stupid having a socket and kept asking why I did it.
I said my reasoning being that a junction box on a new install is RAF and that I couldn't just downgrade the cable size without fusing it down.
I've never been shown a reg saying about the cable size, is this just a preference thing or is it actually what should be done??
 
The overload and fault protection must be adequate for the chosen cable, and load. Why 2.5mm from a fused connection unit? It'll be fused at a maximum of 13a so 1.5 would suffice. If you ran from an FCU then it's fused there isn't it? Nothing wrong with your method though, but effectively the load is fused twice. I often just use a blue Clik connector for the cable to flex joint, with a 3a fuse in the FCU.
Best tell Kev to do one though, are you telling him how to screw a cabinet to the wall?
 
Last edited by a moderator:
Long story short it was one of the legs of the ring til we changed the routing and as it was already hugh level i left this in to be the feed.
I hate that word when describing electrical work "illegal" whenever I get someone telling me they've done their research so know somethings illegal I dunno whether to laugh or slap them
 
So the supply for the hood came from a FCU but you needed to fuse down where the cable connected to the appliance flex ?
Why not fuse appropriately at the FCU ?
 
Personally I just really dont like the idea of a junction box or d box on a new install. I was always taught throughout my apprenticeship and then carried into my years as a spark that when doing a new install any join like that is rough.
 
Its fused at the FCU. I would have out the 3a fuse in there if thay is what you require. Where did you put the socket? If its in view i wouldn't want it in my kitchen either. Its its hidden on top of the cupboards or inside the duct cover from the hood then it makes no difference.
 
Personally I just really dont like the idea of a junction box or d box on a new install. I was always taught throughout my apprenticeship and then carried into my years as a spark that when doing a new install any join like that is rough.
A clik flow plug or a flex outlet plate would be my preference to putting an unnecessary fuse in.
 
Then I cant see what his problem is tell him to worry about his own job. If anything its now easier to isolate if it needs changed. Problem is if it blows it's difficult to change as you have to take the cover off.
This is a very good point, a friend of mine had a stainless chimney type extractor with a plug in behind, GU10 lamp blew and took the fuse out. Kev had mastic'd all round the chimney which made it a right ball ache to get to.
 

Reply to Downgrading cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
795
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
366
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
617

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock