Hi guys.
Run a 10mm to out building for garage board, out building is connected to house and it is twin and earth, as the regs state needs to be rcd protected (less than 50mm etc) but the board i got has an rcd in it to?
So what im asking is there any implications to having 2 rcd's on 1 circuit.
Many thanks guys:)
 
Hey.

With two 30mA RCD's in line there would be no discrimination between the two so in the event of fault there is no way of telling which would trip first.

What I would say is that as you already have 30mA RCD protecting the sub-main then you dont really need another one in the DB at the garage end to protect the sockets and lights as you already have it at the house end.

How is your sub-main cable installed is it surface all the way??
Do you have any spare unprotected ways in your house DB??

You may (depending on various factors) not have to protect the sub-main with 30mA RCD and could have it on normal 32A MCB on unprotected side.

Cheers:D
 
Hey.

With two 30mA RCD's in line there would be no discrimination between the two so in the event of fault there is no way of telling which would trip first.

What I would say is that as you already have 30mA RCD protecting the sub-main then you dont really need another one in the DB at the garage end to protect the sockets and lights as you already have it at the house end.

How is your sub-main cable installed is it surface all the way??
Do you have any spare unprotected ways in your house DB??

You may (depending on various factors) not have to protect the sub-main with 30mA RCD and could have it on normal 32A MCB on unprotected side.

Cheers:D
Thanks for getting back to me.
The cable is run below floor boards and down a wall (about 20mm in) befor going out to were i will be putting new board.
was going to put it on 40amp breaker witch is covered by rcd.
so i should just get new board with a main switch and 6 and 16 or 32 amp breaker??
Once again thanks for your time.
 
Hey mate.

As the sub-main cable needs 30mA protection then a unit as you have described for the garage will be fine.

Just make sure your RCD disconnection times are within limits.

Cheers.:D
 

Reply to Dual rcd???? in the Australia area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
521
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
868
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
661

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock