Where do take the Ze on a dual tariff supply? At the 4 pole isolator (or do you change it to a circuit breaker)at the service head or in the consumer unit?If at the consumer unit which supply, the supply from isolator to consumer unit is a 16mm t&e. Your help will be greatly appreciated.
Technically, you have two installations.
So you can either measure Ze at each board, or if there is a single 4 pole isolator for both boards, you can measure there.
The supplies are in one board and they are fed from the 4 pole isolator. Why I am asking for advice is the 16mm T&E has a 6mm cpc which is obviously not 16mm.
Left hand meter feeds the top Time switch.
The left hand 4 pole isolator isolates the off peak feed from the time clock, and the normal rate feed from the meter.
Then there’s two T&Es from the 4 pole isolator going into the building.
Right hand meter feeds the bottom Time clock and the right hand 4 pole isolator.
Reply to Dual Tariff Supply where do you take the Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...