259
Could do with bit of advice, running a 6mm SWA from consumer unit to shed, where I exit the house will be through the slab foundations straight underground. To do this ill need a long SDS drill bit.

My issue is I would like to use twin walled 40mm underground ducting however I cannot make a 40mm plus hole to get it into the building, obviously I dont want to end it early cause it will fill with water, been trying to find some kind of coupler to attach rigid 25mm conduit that I can get through the hole in the foundations to the 40mm underground ducting but cant find anything.

Anybody know of anything or should I just not bother with the ducting and lay the SWA without ducting, the ducting was only going to be used for extra protection, is this overkill and not worth the hassle?
 
40mm core drill?

Problem is the hole through the foundations needs to be drilled though the cavity so needs to be done at an angle with a meter long SDS drill bit, There is just no way ill get a core drill to drill the hole.. Im thinking maybe a wiskabox underground connecting the two, no terminations but use it like a straight through conduit box.
 

Reply to Ducting reducer or not bother? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So back in the early around year 2000, I was a data networks installer and had a Bosch 24v SDS drill, it was awesome, did pretty everything I...
Replies
12
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
779
I don't think I have worked with 32mm conduit before. Always 25mm and 20mm. I want to contain 2 x 25mm tails and 1 x 16mm earth in some 32mm...
Replies
14
Views
2K
Stroma Certification Scheme Gas and Electric in same underground duct
I need to run gas and electric in underground duct in garden. This is not the supply side, it is the customer side. Wetpants says his regs say...
Replies
12
Views
5K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock