Could you please clear for me the air with earth arrangement I've encountered today. Had a minor electrical work moving sockets and went to check the supply. I can see two earth conductors there. One goes to service head which suggests it's tncs and another connecting to outer sheath of supply cable which suggests tns. Slightly confusing. Any thoughts. Photo attached.
Thanks
 

Attachments

  • IMG_20191127_130150.jpg
    109.2 KB · Views: 116
TNS
The taped up earth is the earth from the split concentric cable connected to the cutout, the exposed blue insulation you can see where it is split gives it away as a split concentric.

This is very badly done and I suspect it may not have been done by the DNO, I would give them a call and get them to check it out.
 
It looks like the TNS earth connection could do with some attention too-is that some form of pipe clamp around the cable?

It is a clamp designed specifically for use on lead cables, but the earth wire has not been fitted in the correct place.
The right hand brass wedge has a cutout in it where the conductor should be placed to hold it firmly against the copper plate.
 
The right side cable looks original (TN-S). The left side cable is newer and is either replacing the original cable which may have become faulty or is a secondary supply to somewhere else, who knows. As above get it checked out.
 

Reply to Earth arrangement photo in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock