As part of my new job, we are required to test existing DC Power Racks for Telecoms. We are told to carry out a earth continuity test, then a IR test, then a ELI test.
I may be getting a little complacent the older I get, but surely Earth Continuity is slightly OTT?
I mean, we're proving an earth when carrying out a ELI test are we not?
I know parallel paths can affect readings etc, but nevertheless I feel its too much. I'd like to hear your thoughts please?
L
 
Of course it's necessary, and you've explained why in your own post.

It's just an R2 test an it takes a matter of min with a wander lead.
 
Is this what the customer has specified?

I'm sure they will have lost expensive electronic equipment to people not following their procedures.
 
so what if you the op miss some thing ,ops fried .

Yes, but but telecoms gear is likely to be able to handle it and it's going to be harder to miss something in telecoms racks where all of the equipment is one place.
Plus you'd hope there's some kind of plan, permit to work system etc in place to make sure that kin dof accident doesn't happen.
 

Reply to Earth Continuity Testing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
622
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
522
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
809
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock