1Justin

-
Arms
Reaction score
157
I did some work today (added a new circuit) to a TT where earth electrode/Ra (bonding disconnected) was 198 Ohms. Bit close to limit where advice is to "investigate".

Interestingly the figure I got is precisely the same as that measured in 2010 by previous electrician, so it does appear to be fairly stable. Maybe grounds to leave it all alone since it's well below 500 (Property has 100mA RCD also on it's PV system) . Despite this I advised householder that probably good idea to re-check frequently, so I put 2 years on my EIC.

Were I to install a new electrode to improve the figure (another reason to upgrade might be that the electrode is a thin mild steel rod, not great looking, and with rust). - Then I believe it's OK (according to GN3) to simply measure Ra for the new one? (We have 30mA RCD's).

Soil type is mostly a sandy area. Alongside the electrode is an old (actually rather nicer) galvanized rod (now disconnected). I get exactly the same figure if I check this one also, which implies it might just be the soil (or they are both equally bad).

Is it the case that if I were to re-install, I could measure only Ra? - Or would I need to get my hands on an Earth Electrode Resistance Tester and do it properly?
 
what is it your wanting to do here Justin?
if its just Ra/Ze you want to measure...then a loop tester will cut it...
if its specific ground resistance you want to measure....then you need a ground resistance tester....
its a 4 wire test as well is that....
 
Am I right in thinking that a four wire ground resistance tester would only be necessary on a empty (no supply) field site prior to DNO setting a supply?

As I have a supply, and a house, and just a dodgy looking electrode, then do I just bang in a new one (should I want to ), and measure Ra with standard high current Ze/loop tester?
 
yep...use the high current setting on the loop tester....
alternatively you could get an earth resistance tester....but then you need the test leads and spikes to go with it.....can be pricy...
use your loop tester Justin....go for a min. of 2 X 5/8" rods....site em well....say about a meter or so from any structures....and someware theres going to be no digging activity....
also protect the main earth cable with a leg of conny....
 
Hi Glenn,

Thanks for that. Useful tips.

BTW I got one of those mini current clamps you recommended a few weeks ago. Nice little instrument, works well :)
 
Interestingly the figure I got is precisely the same as that measured in 2010 by previous electrician, so it does appear to be fairly stable. Maybe grounds to leave it all alone since it's well below 500

From where did you get the 500 ohms as being the maximum from?? Even the numpty recommendation in the BGB is 200 ohms, and your value is only 2 ohms below that figure!!

Bare steel and galvanised steel electrodes are not ideal by a long choc for many different soil conditions, sandy soils would be one of them. Copper clad steel rods are pretty much immune (within reason) to all soil conditions, as far as accelerated corrosion is concerned, and have a far better conductivity value than steel, galvanised or otherwise.
 
That sandy soil is crying out for some proper rodding...Put one in recently in sandy soil with red clay strata 2m down,got three 5/8ths in with old Hilti TE72 in 40 minutes.Conditions dry now but 8 ohms,will probably get to retest in Winter.Go on,get piling....
 
I did some work today (added a new circuit) to a TT where earth electrode/Ra (bonding disconnected) was 198 Ohms. Bit close to limit where advice is to "investigate".

Interestingly the figure I got is precisely the same as that measured in 2010 by previous electrician, so it does appear to be fairly stable. Maybe grounds to leave it all alone since it's well below 500 (Property has 100mA RCD also on it's PV system) . Despite this I advised householder that probably good idea to re-check frequently, so I put 2 years on my EIC.

Were I to install a new electrode to improve the figure (another reason to upgrade might be that the electrode is a thin mild steel rod, not great looking, and with rust). - Then I believe it's OK (according to GN3) to simply measure Ra for the new one? (We have 30mA RCD's).

Soil type is mostly a sandy area. Alongside the electrode is an old (actually rather nicer) galvanized rod (now disconnected). I get exactly the same figure if I check this one also, which implies it might just be the soil (or they are both equally bad).

Is it the case that if I were to re-install, I could measure only Ra? - Or would I need to get my hands on an Earth Electrode Resistance Tester and do it properly?

Cant possibly be stable though.....well, according to ....?
 
ignoring the old fossils for a moment........ :)

as for the OP's original enquiry regards getting a dedicated ground resistance meter , its not really worthwhile for your average jobbing spark.
The IET and all their official literiture now all but endorse the earth loop method of checking Ra as an acceptable alternative.
 
Hi Engineer54

From where did you get the 500 ohms as being the maximum from?? Even the numpty recommendation in the BGB is 200 ohms, and your value is only 2 ohms below that figure!!

By my understanding, 200 Ohm is recommended for investigation (ie is it stable..). The well known 1666 ohms max for 30mA RCD (= 50V/30mA) and for 100 ma RCD (which customer has on PV system) 500 ohms (=50V/100mA). See GN3 Pg 48.

QED?

Rgds
 
Hi Engineer54



By my understanding, 200 Ohm is recommended for investigation (ie is it stable..). The well known 1666 ohms max for 30mA RCD (= 50V/30mA) and for 100 ma RCD (which customer has on PV system) 500 ohms (=50V/100mA). See GN3 Pg 48.

QED?

Rgds
200 ohms is the max value whilst the Ra will remain stable....
its a case of the Ra increasing by up to 8 times (worst case)....so 8 X 200 is 1600....so still under the value of 50V/0.03 = 1667
but in reality its a con....
the NIC say 100 ohms....
again..a con....
 
Hi Engineer54



By my understanding, 200 Ohm is recommended for investigation (ie is it stable..). The well known 1666 ohms max for 30mA RCD (= 50V/30mA) and for 100 ma RCD (which customer has on PV system) 500 ohms (=50V/100mA). See GN3 Pg 48.

QED?

Rgds

The very last place i would take advice from on any TT system is BS7671 or it's OSG's, Wirepuller is your man here!!

If both the house and the PV system is TT, id be asking why has the PV system been given a 100mA RCD and the house 30mA...?? If the house is on a TN system, again, why they have thought it necessary to TT the PV system?
 
Hi Engineer54



By my understanding, 200 Ohm is recommended for investigation (ie is it stable..). The well known 1666 ohms max for 30mA RCD (= 50V/30mA) and for 100 ma RCD (which customer has on PV system) 500 ohms (=50V/100mA). See GN3 Pg 48.

QED?

Rgds
You are correct Justin,it comes down to whether or not you accept the 7671 values/recommendations.
I get slated on here for accepting those....by the very same people who also slate the reliance on RCD's as primary earth fault protection and yet fall over themselves to praise an Ra of 15 ohms!'
Either accept higher Ra values and reliance on RCD's, or obtain a stable TN value of Ra and back up RCD's with effective OCPD earth fault protection. There's no in-between', despite the 'holier than thou' rubbish spouted by certain members on this subject.
 
You are correct Justin,it comes down to whether or not you accept the 7671 values/recommendations.
I get slated on here for accepting those....by the very same people who also slate the reliance on RCD's as primary earth fault protection and yet fall over themselves to praise an Ra of 15 ohms!' Normally you quote 10 ohms?? ...anyway it's only you falling over yourself seeing, or rather wanting to see something that's never been implied or stated. Either accept higher Ra values and reliance on RCD's, or obtain a stable TN value of Ra and back up RCD's with effective OCPD earth fault protection. There's no in-between', despite the 'holier than thou' rubbish spouted by certain members on this subject.

Say's the man that only talks about spikes for sheds and garages!! lol!!

I don't get paid good money to run multi million dollar projects by spouting rubbish!! I'll leave all the rubbish spouting, to the clever but lazy buggers that openly wouldn't even try to install a decent TT system, and fall back on the crap that written in the BGB...
 
New posts

Reply to Earth electrode tester or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
397
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
968
I have a PeakTech Digital resistance tester for sale, still in it original packaging, never used, cardboard box is a bit shop soiled, but the...
Replies
2
Views
247
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock