Can some one help sharing an example on how Earth Fault impedance can be calculated for an underfloor busbar.

After testing the earth fault impedance for the circuit it is showing higher impedance than the max value.

Thanks
 
Can some one help sharing an example on how Earth Fault impedance can be calculated for an underfloor busbar.

After testing the earth fault impedance for the circuit it is showing higher impedance than the max value.

Thanks

Don't forget that if the usual methods (supplementary bonding, rcd protection etc.) aren't practical, you can use manufacturers maximum Zs values which usually have a better max value X80% for rule of thumb.
Just make a note on your EIC.

(R1+R2) values on busbar systems are normally comparably small due to the CSA of the conductors-are you starting off with a high Zs before the busbar or using type 'D' MCB's?
 
Thank you for the response...breaker (MCB) is Type "C", length of run is 28.8m, earth size cable is 10mm2, circuit breaker is 32A, and on the test meter I am getting 0.86 ohm of Zs which is greater than the max impedance..
 
Can you change to a type B?.....max 1.15(off top of head).....or if RCD'd 1667 becomes the max.......based on the info given though, as Mr IQ states the Zs would perhaps be a little high at the origin of the circuit.
 
From the size of conductors and length you have stated i would of said that should be well within max zs, i think u may have issues with main earth have u taken a ze reding yet, or ra if its tt ? also on ur meter are you testing in high current mode or non trip ? if you have that facillity anyway ?
 
Last edited by a moderator:
From the size of conductors and length you have stated i would of said that should be well within max zs, i think u may have issues with main earth have u taken a ze reding yet, or ra if its tt ? also on ur meter are you testing in high current mode or non trip ? if you have that facillity anyway ?

I doubt main earth issues, this could be a sub-circuit from a distribution circuit, from a section board on a TN-S system with a max Ze of 0.8 Ohms, we're only talking 0.86 Ohms at the end of all that!
 
Thanks for all replies...

This is one of 4 circuits, others are measuring around 0.93, can someone post a sample of calculation on how it should be measured.
 
Your question is not making sense to me. You don't need to calculate it if you are measuring it. If your measurement it is too high to give a satisfactory disconnection time against the tabulated rating for your protective device, then you should change either the bonding arrangements or use a different device. The only calculating you may need to do is adding or subtracting the loop tests at different points along the circuit to establish if and where best to introduce additional bonding if that is your chosen method of addressing the problem. You may wish or need to use R1+R2 for some of these measurements, but, at the end of the day, it is the Zs at the furthest point of utilisation that needs to be satisfactory.
If it isn't making sense you could call in an electrician for an hour or so and watch, ask and learn for less than £40.
 

Reply to Earth Fault Impedance in the Australia area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
513
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
407
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
702
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock