Hi Guys came across this one when I was installing a bathroom fan. When I took the old fan down which had blown, I tested the wires and noted the following; Between active and neutral 240 between active and earth 120v the same on the Switched Active but when I turned off the lights the voltage incresed to 227v. Does this mean I have a fault to earth?

Cheers for any help

-Michael
 
Thats what I thought. Any suggestions? Does this mean I have an active conductor in contact with earth somewhere in the circuit? If so why would it be dropping when the I turn the lights on, I mean I could understand the switched active, but why would the active be influenced by the light switch?
 
You could IR test the circuit in question mate............Test between all conductors and make sure that when you do that nowt else sensitive is connected to the circuit you are testing (so isolate the circuit under test from any others first wont you mate).............
 
Thats what I thought. Any suggestions? Does this mean I have an active conductor in contact with earth somewhere in the circuit? If so why would it be dropping when the I turn the lights on, I mean I could understand the switched active, but why would the active be influenced by the light switch?

You're very active. :D

They're called line conductors​ these days.
 
The lighting circuit is full of low voltage transformers, do they affect IR readings? If there is a voltage drop does this mean its dropping across something not earthed? If there is a fault to earth why would breaker not trip?
 
The lighting circuit is full of low voltage transformers, do they affect IR readings? If there is a voltage drop does this mean its dropping across something not earthed? If there is a fault to earth why would breaker not trip?
trannys are ELV mate (extra low voltage) dont forget terminology here.......How many loads are connected and how longs the cable run and what size is it?..........the problem with radials is you get volt-drops appearing as length increases and loads are applied.....
 
Darkle,

start at the begining check at the mains first I had this the other day 210 volts at the end of line

found 210 coming in some times over thinking blinds us just a thought

also I find as Glennspark says do some basic checks get it clear in your head good luck
 

Reply to Earth Fault? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock