your thoughts please got called to the in laws resturant fault was sqrews on light switch were live ok so i tested and true enough 230v on sqrews the light switch was a combined mem emergency one way and a 1 way switch changed switch but still happening when the switch is off its ok when switch is on theres 230v on sqrews so up in the gods ie high ceiling with no access at moment is 3 twin light fitting plus 2 running men lights now one of the fittings ballast has burnt out with only one lamp working in the fitting now my guess is am i getting a fault through this ballast and why hasnt it taken out the mcb and yes i have earth continuity back at db once the scaffold is returned to site i can get up to the fittings to find out exactly what is the problem
 
When you say that you have earth continuity I take it that is from the switch screws back to the cu.
 
i no further investigation is required but cant get up to lights without scaffold changed switch and sqrew heads have them white caps over them so no one is exsposed to live sqrews cant understand why it wouldnt take 6amp mcb out
 
If the screws are live, then there is no earth on the Back box and screws.

If the screws are only live when the switch is on, the live originates from that switch wire.

The Mcb won't trip as there is most likely no earth at the fitting/s either and the ballast had melted a live to fitting casing.
 
Sounds like a strange one lol. When you tested voltage at the screws what did you have the second probe touched on to? Was there a neutral at the switch?
 
snowhead the switch is a patrass all in pvc tube there are 2 earths at switch which are connected to light switch grid your right the switch wire is the problem and there is earths at fittings as i installed the installation about 8 years ago
 
sintra i tested from sqrews to metal dish washer locally were everthing in kitchen is earthed

Sounds like the screws aren't earthed then if you have used an earth as your reference point.
 
The switch grid is connected to "earth" I assume?
I'd still go for you've lost the earth back to the D.B and it's live to "Earth" in the fitting feeding back down to the switch.

Watch out when up the scaffold if the light fittings are live......
 
there's a thread from yesterday where an EDF "engineer" waved a volt stick next to a water pipe and said it was live because his volt stick lit up.
 
your thoughts please got called to the in laws resturant fault was sqrews on light switch were live ok so i tested and true enough 230v on sqrews the light switch was a combined mem emergency one way and a 1 way switch changed switch but still happening when the switch is off its ok when switch is on theres 230v on sqrews so up in the gods ie high ceiling with no access at moment is 3 twin light fitting plus 2 running men lights now one of the fittings ballast has burnt out with only one lamp working in the fitting now my guess is am i getting a fault through this ballast and why hasnt it taken out the mcb and yes i have earth continuity back at db once the scaffold is returned to site i can get up to the fittings to find out exactly what is the problem
Jeez, has someone stolen your comma and full-stop keys?? Ha ha, sorry - couldn't resist. Daz
 

Reply to earth fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
514
Suggestions / solutions please anyone? I have a 2 way switch, Hall and Landing, power being fed on Landing. When the switch is turned on, the...
Replies
2
Views
487
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
785
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
586
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
773

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock