Just done a periodic on a farm cottage with TT.
Installed a MET as there was just an odd brass clamp before. The main earth is a black cable approx 6mm
I can't find where or to what it is connected, however the Ze reading is 3.56 ohm.
My question is this; do I put a new earth rod in (the best reading I have ever achieved is 17.3 ohm) or do I leave it as is ? as 3.56 is very low. I changed the 100mA rcd for a new 30mA feeding a nasty Wylex fuse board, but circuits all tested out ok.
Any thoughts ?