Just done a periodic on a farm cottage with TT.

Installed a MET as there was just an odd brass clamp before. The main earth is a black cable approx 6mm
I can't find where or to what it is connected, however the Ze reading is 3.56 ohm.
My question is this; do I put a new earth rod in (the best reading I have ever achieved is 17.3 ohm) or do I leave it as is ? as 3.56 is very low. I changed the 100mA rcd for a new 30mA feeding a nasty Wylex fuse board, but circuits all tested out ok.
Any thoughts ?
 
Hi.

If it were me and I couldn't confirm the presence of an electrode Then I would definately be installing a new one.

3.56 does seem a bit too low for a rod, it could be lashed onto anything.
 
New rod should ideally be put in as you need to be able to verify it and its connections.

30mA RCD no good on the whole CU as you have no circuit separation if a fault occurs. It will take out the whole house.
 

Reply to Earth rod or not ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
981
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
855
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock