I have just carried out an EICR.

Earthing is TT. A 4mm green/yellow conductor leaves the CU and disappears under the conservatory, I get 158Ω when I do a Ze test.

There is a 10mm that goes to both gas and water. ZS tests are around 40Ω 's on sockets/lights.

I started a similar thread some time ago Unable to find earth rod when doing EICR - https://www.electriciansforums.net/threads/unable-to-find-earth-rod-when-doing-eicr.169576/page-6 which caused lots of discussion and most people erred towards a C3, although NV, LIM and FI were all mentioned, showing that it is a difficult one to code.

I just can't get my head around giving it a C3. It could be classed as the single most important conductor of the whole installation and I can't even get to the termination on the 'possible' earth rod to check it's ok. The termination could be appalling, I could have got 158Ω even if the 4mm conductor was just resting on the earth rod. I was going to say this is highly unlikely, but I have seen some pretty terrible terminations. Also, if the builders didn't have the knowledge to leave it accessible then I doubt they took much care when building around it. Also, builders tend to think earthing/bonding cables are not important and often just chop them off, so again, they could have done anything to it.

When I had to code serious incidents in another profession we looked at 2 influences to get a 'danger' rating.

Likelihood of occurrence and severity if it does occur.

In this case the likelihood is low (i.e termination becomes poor, may not even be an earth rod there, etc etc) but the severity is high (i.e RCD does not operate and therefore possible death under fault conditions)

I think this has to be a C2.

Putting it as an operational LIM is just ignoring the problem. NV is again ignoring the problem. FI..... possibly, but I've already investigated and the rod cannot be found.

I just need to put a new rod in, but with a C3 this may well not happen.

Would you guys still think C3??
 
Hmmm, if I can’t see it then FI for me.

I have a job underway to add a circuit and the rod results in about 70 Ohms, but it’s been covered by an extension and flooring, I think... Long story short, I have now quoted to add another rod. After confirming the new one works I’ll likely leave both connected at the MET as the invisible one is clearly working as present.
 
Probably C3 on the basis that there is a acceptable measurement so some sort of electrode!, but improvement recommended (ie a new cable/rod as required for compliance) as currently it cant be visually verified. Personally, I don't see it as 'requiring urgent remedial works'.
C2 if higher than 200ohms
Highlight it and recommend a short interval between next inspection(s) so it can be monitored more frequently! Its probably been like it for years so another 6-12months probably wont make much difference.
 
FI.... even if it mean digging the floor up. It’s the only way to be 100% sure.

Other than that, belt in a new rod in an easier place.

Hmmm, if I can’t see it then FI for me.

I have a job underway to add a circuit and the rod results in about 70 Ohms, but it’s been covered by an extension and flooring, I think... Long story short, I have now quoted to add another rod. After confirming the new one works I’ll likely leave both connected at the MET as the invisible one is clearly working as present.
So even though you both disagree on the exact code, you still think it is potentially dangerous. A FI implies that you think it may be a C1 or C2, as if you think it's a C3 you wouldn't FI. Also, if you are going to put in another earth rod (for a customer) you must think it's potentially dangerous as it is, otherwise it could just stay as it is.

It's difficult isn't it!
 
Probably C3 on the basis that there is a acceptable measurement so some sort of electrode!, but improvement recommended (ie a new cable/rod as required for compliance) as currently it cant be visually verified. Personally, I don't see it as 'requiring urgent remedial works'.
C2 if higher than 200ohms
Highlight it and recommend a short interval between next inspection(s) so it can be monitored more frequently! Its probably been like it for years so another 6-12months probably wont make much difference.
It may be <200 now, but it could be incredibly unstable as I can't access it to see the termination. Regular checks would be a good idea, but no customer is going to pay you to come out every 6-12 months.

I still think it has to have a new rod, but this can only be guaranteed by giving it a C2.

Again, this is such an important conductor that I don't think we can use terminology like 'probably', it needs to be 'incredibly likely' or 'definitely'. Even though you're probably right ?
 
FI has in this case proved impracticable, without causing damage to property.
Best practice guide 4 recommends C2 for absence of a reliable and effective means of connection to earth.
The way I see it in this case:
1. You can't prove that it's not absent
2. You can't prove it is reliable and effective from just one measurement, and it's a bit on the high side.
Therefore you don't have a reliable and effective means of earthing, therefore it's a C2.
Therefore install a new earth electrode.
 
FI for me is the most appropriate conclusion. New Earth electrode is the most realistic course of action for remediation.
but he 's done the FI already, can't find the rod. can't investigate further without a kango.
 
but he 's done the FI already, can't find the rod. can't investigate further without a kango.
He mightn't be able to investigate further without a kango, but that doesn't change the fact that without further investigation we don't know for certain whether it's OK or not.

So as I say it's an FI for me - but I would have no issue with someone else putting it as C2 if they prefer. You could put accessibility of the connection as a C2 and the condition of the electrode as an FI if you liked, I suppose.
 
I wasn't aware an RCD needed a connection to earth to operate correctly.
The RCD might not need an earth rod as such, but it only trips if there is a low enough path to earth. If they are all 30mA instant RCD/RCBO then if it is you form that path then you should not die, but if some are on a 100mA delay incomer then its a different game. But there ought to be a path so if a fault occurs it trips before you tocuh the offending circuit.

Also the system is designed to have an earth. In fact the ESQCR (I think) make a means of earthing mandatory, so the absence of a reliable earth is at least a C2 even with RCD being present.
 
I have just carried out an EICR.

Earthing is TT. A 4mm green/yellow conductor leaves the CU and disappears under the conservatory, I get 158Ω when I do a Ze test.

There is a 10mm that goes to both gas and water. ZS tests are around 40Ω 's on sockets/lights.

I started a similar thread some time ago Unable to find earth rod when doing EICR - https://www.electriciansforums.net/threads/unable-to-find-earth-rod-when-doing-eicr.169576/page-6 which caused lots of discussion and most people erred towards a C3, although NV, LIM and FI were all mentioned, showing that it is a difficult one to code.

I just can't get my head around giving it a C3. It could be classed as the single most important conductor of the whole installation and I can't even get to the termination on the 'possible' earth rod to check it's ok. The termination could be appalling, I could have got 158Ω even if the 4mm conductor was just resting on the earth rod. I was going to say this is highly unlikely, but I have seen some pretty terrible terminations. Also, if the builders didn't have the knowledge to leave it accessible then I doubt they took much care when building around it. Also, builders tend to think earthing/bonding cables are not important and often just chop them off, so again, they could have done anything to it.

When I had to code serious incidents in another profession we looked at 2 influences to get a 'danger' rating.

Likelihood of occurrence and severity if it does occur.

In this case the likelihood is low (i.e termination becomes poor, may not even be an earth rod there, etc etc) but the severity is high (i.e RCD does not operate and therefore possible death under fault conditions)

I think this has to be a C2.

Putting it as an operational LIM is just ignoring the problem. NV is again ignoring the problem. FI..... possibly, but I've already investigated and the rod cannot be found.

I just need to put a new rod in, but with a C3 this may well not happen.

Would you guys still think C3??
You've rationalised it very well, hazard, liklihood and consequence.

The 158Ohms Ze hints at a poor connection, corroded rod, poor ground conditions but ultimately the quality of this rod cannot be verified.

FI will not show anything without invasive works.

NV is a cop out.

C3 will record your findings and coupled with a short retest date may force the owners hand but may likely be ignored.

C2 forces the owner to rectify, and it needs rectifying.

I'd go C2 but its very grey.

My very first earth rod was for the same situation and similar iffy Ze, not absolutely mandated but absolutely necessary.
 

Reply to Earth rod 'probably' buried under conservatory, which code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Come across this a couple of times recently whilst doing eicr’s. Everything all ok except there is no access to the (presumably) earth rod. The...
Replies
4
Views
4K
Just a bit of a muse at the moment, work won't happen for a while, though I do already have the ducting. We have (what's left of - it was rotten...
Replies
0
Views
1K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock