• Please checkout this (ad-free) update post I've done on a spare blog. Feel free to bookmark it and check everynow and again for update if ads are pissing you off. Always feel free to ad-block them for now though if you want. I'll let you know when you can disable the ad blocker again, only if you want to see the ads. They should look nice and neat in the end.

Discuss Earth rods to reduce Ze in the Electrical Forum area at ElectriciansForums.net

M

Marxman99

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Can anyone help.
The electrician has measured the Zs of a new submains cable installation and it is too high.
The set up is this:
We have a new external cabinet housing a 200A 3phase TN-S intake. From the intake 1 new 150metres 95mm sq 4core swa + sep 35mm sq earth cable has been run to a main switch in a switchroom. In this main switch we wanted to install 200A BS88 fuses but the Zs fails. The recorded Zs is 0.29ohms (IEE regs allows 0.19ohms max for 200A BS88 fuse). The Ze at the intake position is 0.22ohms. We do not want to use an RCD on any point of the network. How can earth rods be implemented?
This is the link to the photos:
https://dl.dropboxusercontent.com/u/19108813/1_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/2_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/3_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/4_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/5_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/6_main switchroom.JPG
https://dl.dropboxusercontent.com/u/19108813/7_main switchroom.JPG
https://dl.dropboxusercontent.com/u/19108813/8_main switchroom.JPG
Regards
 

D Skelton

-
Mentor
Esteemed
Arms
Reaction score
3,568
I can tell you now without doing any calculations that the 95mm cable has been incorrectly selected, especially for volt drop! Regardless of that, Zs compliance will be achieved by increasing the size of those conductors, or by lowering the size of the fuse.

This smells to me to be nothing short of a monumental balls up by the electrician, who obviously has no design knowledge whasoever! I'd seriously consider getting someone in who knows what they're doing!
 
Reaction score
3,769
I can tell you now without doing any calculations that the 95mm cable has been incorrectly selected, especially for volt drop! Regardless of that, Zs compliance will be achieved by increasing the size of those conductors, or by lowering the size of the fuse.

This smells to me to be nothing short of a monumental balls up by the electrician, who obviously has no design knowledge whasoever! I'd seriously consider getting someone in who knows what they're doing!

it does sound a bit small even without volt drop.

4 core 95mm swa gives about 165amps in direct in ground/ducting.

in free air/perforated tray it gives 250amps.

obviously without any derating factors or voltdrop
 

Darkwood

Staff member
Mod
Mentor
Esteemed
Arms
Reaction score
10,194
The Zs required is stated wrong too the tables show 0.19ohms for a 200amp BS88 but have you applied 0.8 factor which will require a 0.15ohms to comply.

From your forum history on here - 3 yrs ago you were doing an Electrical Engineering course and asking about designing a supply system for a backed-up server system, this implies your courses were heavy with installation and cable calcs of supply systems .... with all due respect then regarding your history I would have thought you would be the one helping others as oppose to asking such a question.

When you say 'The Electrician' measured.... What was his role in this job, did he design, install the supply and may I asked what was your role in the job and why are you getting involved if others have made big errors?

And as above its sounds a monumental cock-up in design ...like a calculation has never been applied to the cable for derating factors!

The 200amp fuses overate the CCC of the cable by a large marging
Volts drop does not comply

When the cable set on fire through overload and the front end fuses only operate on the cables destruction then who's name is on the design of the installation???

and you thought your biggest issue was Zs here!!!!!
 
Last edited:
OP
E

Engineer54

How can earth rods be implemented?

Seriously, with great difficulty!! You're trying to reduce an already relatively low Ze value of 0.22 ohms with earth rods!! So you're going to need a good few of them. ...lol!! Do you know how close you are to the supplying DNO distribution Transformer?? Also a good chance that DNO TN-S Cable is probably derived from an old TN-S network cable that's been PME'd....
 

Reply to Earth rods to reduce Ze in the Electrical Forum area at ElectriciansForums.net

Similar Threads

Today I found a 466 ohm Ze. That's actually a new upper record for me. I assume the rod was completely corroded through. So started to bang in...
Replies
24
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
2K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
2
Views
716
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
4K
I have a job where the Ze is at 8.38 OHMS it was at 50.48 OHMS i have installed a new Earth rod but cant bring it down anymore has anyone got any...