Can anyone help.
The electrician has measured the Zs of a new submains cable installation and it is too high.
The set up is this:
We have a new external cabinet housing a 200A 3phase TN-S intake. From the intake 1 new 150metres 95mm sq 4core swa + sep 35mm sq earth cable has been run to a main switch in a switchroom. In this main switch we wanted to install 200A BS88 fuses but the Zs fails. The recorded Zs is 0.29ohms (IEE regs allows 0.19ohms max for 200A BS88 fuse). The Ze at the intake position is 0.22ohms. We do not want to use an RCD on any point of the network. How can earth rods be implemented?
This is the link to the photos:
https://dl.dropboxusercontent.com/u/19108813/1_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/2_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/3_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/4_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/5_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/6_main switchroom.JPG
https://dl.dropboxusercontent.com/u/19108813/7_main switchroom.JPG
https://dl.dropboxusercontent.com/u/19108813/8_main switchroom.JPG
Regards
The electrician has measured the Zs of a new submains cable installation and it is too high.
The set up is this:
We have a new external cabinet housing a 200A 3phase TN-S intake. From the intake 1 new 150metres 95mm sq 4core swa + sep 35mm sq earth cable has been run to a main switch in a switchroom. In this main switch we wanted to install 200A BS88 fuses but the Zs fails. The recorded Zs is 0.29ohms (IEE regs allows 0.19ohms max for 200A BS88 fuse). The Ze at the intake position is 0.22ohms. We do not want to use an RCD on any point of the network. How can earth rods be implemented?
This is the link to the photos:
https://dl.dropboxusercontent.com/u/19108813/1_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/2_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/3_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/4_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/5_external intake cabinet.JPG
https://dl.dropboxusercontent.com/u/19108813/6_main switchroom.JPG
https://dl.dropboxusercontent.com/u/19108813/7_main switchroom.JPG
https://dl.dropboxusercontent.com/u/19108813/8_main switchroom.JPG
Regards