TJC1

-
Reaction score
6
Got chatting to another electrician today who said about using 16mm earth for TT. Not that i have ever had to put steak in but am i right in saying its 10mm for a TT system?
 
it's 2.5mm min. if protected mechanically and against corrosion. and my steak is in the pan, ready to cook with chips.
 
I would be happy to use 2.5 mm protected :)
I suspect any reduction of earth resistance by using larger size cable to ground (other than for reasons of mechanical protection) is minimal,driving in longer electrodes would probably help,but why go to all the trouble when the cable generally only needs to carry 30 m/amp to operate a RCD,your 10mm should be fine if your not burying
 
I would also be inclined to use 10mm
as above, it has more physical strength, who really wants to add mechanical protection to a cable so they can save £5 on the job?
10mm is always on the van so it just seems like a good choice for 99% of the jobs.
 

Reply to Earth size for TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
492
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock