so bond the lead pipe. easy sweat a connection to that. even a plumber could do it.
 
I think that is his question: should the incoming lead pipework be bonded?

Probably the boiler no longer requires bonding, but no point in removing it either. However, the lead pipe, stopcock, and filter are all extraneous parts and accessible to touch so should be bonded.
[automerge]1591462066[/automerge]
Ah, just missed your reply!
 
looks like the plastic has eliminated the need for bonding. the only extraneous metal pipework appears to be the incoming up to the plastic. test any copper to MET. above 22k Ohms, not extraneous. if < a couple ohms, it's bonded elsewhere, e.g. to the gas at the bolier. and what's that torpedo above the stop. is it a filter?
but should the lead pipe up to the plastic tee not be bonded as it can be touched
[automerge]1591462718[/automerge]
so bond the lead pipe. easy sweat a connection to that. even a plumber could do it.
is there no suitable clamps for lead
 
there will be a washing machine going there
so... unless you pull the machine out and it simultaneously develops an electrical fault whilst you are turning off the water stop cock, at the same time a pink pig is flying past the window, riding on a winged elephant?????
 
so... unless you pull the machine out and it simultaneously develops an electrical fault whilst you are turning off the water stop cock, at the same time a pink pig is flying past the window, riding on a winged elephant?????
i know, my problem is that i dont fully understand in my head what earth actually is i just think everthing needs bonding together and not fully understanding it all, but thanks for your input most appreciated.
i have looked on youtube trying to find earthing for dummies.
 
If the lead pipe supplies drinking water, I'd be inclined to replace it. A length of MDPE pipe and no more worries over bonding or lead contamination :D
that would entail a lot of digging up. all the way back to the water main in the strreet, which is probably rusty iron anyway.
 
found this on the internet it mentions if you have an incoming plastic water pipe you do not need to main bond, however if the rest of the pipework there after is metal you will require main earth bonding, i have highlighted it. this is driving me mad any one shed some light please.
 

Attachments

  • earthbonding.pdf
    96.5 KB · Views: 5
You do not have an all insulated service pipe. This thread has become over complicated, that lead pipe requires a main protective bond.
 
I'll try and shed some light for you.
In the event of a fault on your electrical system conductive parts (ie earthed metal parts of the electrical installation such as a metal light fitting or washing machine case) may experience a rise in potential relative to the general mass of earth which is at zero volts or thereabouts. Within a building that rise in potential is unlikely to be a serious hazard because a person in contact with a conductive part during the fault is likely to be stood on an electrically insulating surface such as a wooden floor. However the metallic water service is in contact with the general mass of earth and will introduce that potential into the building. Now there is a hazard because a person may be in contact with both a conductive part and the water service at the same time the fault is in progress and subject to a shock. By bonding both together the possibility of a potential difference is reduced. Where there is an insulating section immediately after the water service enters the property the rest of the copper pipework in the house has effectively been disconnected from the general mass of earth and so does not require bonding because it can no longer introduce an earth potential.
In your case the rest of the house pipework is isolated from the earth potential by the plastic joint, only the short section of lead and the filter are extraneous. As Tel stated what are the chances of contact between that and a conductive part for the duration of a fault? If you think there is then bond the lead. But you DO NOT NEED TO BOND THE REST OF THE PIPEWORK AFTER THE PLASTIC JOINT. In fact doing so may actually increase the shock risk in the event of a fault.
[automerge]1591478252[/automerge]
last one promise, the rest of the copper in the installation after the plastic tee still requires main earth bonding no
NO!
 
I'll try and shed some light for you.
In the event of a fault on your electrical system conductive parts (ie earthed metal parts of the electrical installation such as a metal light fitting or washing machine case) may experience a rise in potential relative to the general mass of earth which is at zero volts or thereabouts. Within a building that rise in potential is unlikely to be a serious hazard because a person in contact with a conductive part during the fault is likely to be stood on an electrically insulating surface such as a wooden floor. However the metallic water service is in contact with the general mass of earth and will introduce that potential into the building. Now there is a hazard because a person may be in contact with both a conductive part and the water service at the same time the fault is in progress and subject to a shock. By bonding both together the possibility of a potential difference is reduced. Where there is an insulating section immediately after the water service enters the property the rest of the copper pipework in the house has effectively been disconnected from the general mass of earth and so does not require bonding because it can no longer introduce an earth potential.
In your case the rest of the house pipework is isolated from the earth potential by the plastic joint, only the short section of lead and the filter are extraneous. As Tel stated what are the chances of contact between that and a conductive part for the duration of a fault? If you think there is then bond the lead. But you DO NOT NEED TO BOND THE REST OF THE PIPEWORK AFTER THE PLASTIC JOINT. In fact doing so may actually increase the shock risk in the event of a fault.
[automerge]1591478252[/automerge]

NO!
im finally starting to get it thanks for finding the time and effort explaining this most appreciated
 
Main bonding should be on the consumers side of the stopcock, the lead pipe is before the stopcock, therefore the bond should be on the copper and not the lead.
It should be but as can be seen from the picture that is not really possible. If the OP feels the need to bond the short section of extraneous lead before the insulating joint I see no reason why it cant go on the lead.
 

Reply to Earthing Arrangement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
877
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
430
What are the regulations requirements on Earth bonding ? I am currently planning a 1st fix re wire I have the following setup Gas Meter...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock