What should a certain member do?

As far as I know. If EV fitted on an actual building that has PME, it can be connected to PME. However if fitted remotely, has to be TT. Others may differ though

Also, if TT Ra reading to be as low as possible. Best below 100 ohms. If around 150 ohms vehicle may not charge.
 
Last edited:
I am pleased with the way the other thread has progressed, its actually got to over 300 posts without any abuse etc, its been really productive.

The way i am going to do it is assess the Ra of the Steel structure and accept that as a form of TT.
 
UK, have you not understood anything we have being saying to you ?

You have a few options,

1) ensure the three Phase supply is balanced according to the formula in the associated annexe with exemption I), and then it doesn't really matter how good the building is earthed to true earth, the load balancing alone will prevent the N/PME Earth from rising above 70V in the case of a broken suppliers N, you just use the existing earthing system for this method, as per the Niccys advice, if the building and services happens to be in fortuitous contact with true earth so much the better, but you are relying on a balanced system as the main method of compliance via exemption I)

2) add additional rods to the PME MET to achieve the same ends, you need an extremely low Ra for this method at about circa 1 or 2 ohms, this is nothing to do with TT

3) supply it from a 1:1 isolation transformer, meaning a fully floating supply
You cannot TT it due to the proximity of the PME bonded metal building
 
Last edited:
UK, have you not understood anything we have being saying to you ?

You have a few options,

1) ensure the three Phase supply is balanced according to the formula in the associated annexe with exemption I), and then it doesn't really matter how good the building is earthed to true earth, the load balancing alone will prevent the N/PME Earth from rising above 70V in the case of a broken suppliers N, you just use the existing earthing system for this method, as per the Niccys advice, if the building and services happens to be in fortuitous contact with true earth so much the better, but you are relying on a balanced system as the main method of compliance via exemption I)

Fine to a point, if you can balance the phases the chances of achieving a perfect or near perfect balance will in reality be neigh on impossible...

2) add additional rods to the PME MET to achieve the same ends, you need an extremely low Ra for this method at about circa 1 or 2 ohms, this is nothing to do with TT

This is the only real solution in my opinion!!

3) supply it from a 1:1 isolation transformer, meaning a fully floating supply
You cannot TT it due to the proximity of the PME bonded metal building

More dangers here than without an isolation TX. Not recommended!!

My comments in italics

 
UK, have you not understood anything we have being saying to you ?

You have a few options,

1) ensure the three Phase supply is balanced according to the formula in the associated annexe with exemption I), and then it doesn't really matter how good the building is earthed to true earth, the load balancing alone will prevent the N/PME Earth from rising above 70V in the case of a broken suppliers N, you just use the existing earthing system for this method, as per the Niccys advice, if the building and services happens to be in fortuitous contact with true earth so much the better, but you are relying on a balanced system as the main method of compliance via exemption I)

2) add additional rods to the PME MET to achieve the same ends, you need an extremely low Ra for this method at about circa 1 or 2 ohms, this is nothing to do with TT

3) supply it from a 1:1 isolation transformer, meaning a fully floating supply
You cannot TT it due to the proximity of the PME bonded metal building

1. I am just waiting for Amazon to deliver my book to day so will look at (i) then and calculate it.

2. I could put rods in, but what is it actually going to achieve on the basis the steel of the building is already doing the same job? I am not against the idea, but want a rock solid explanation as to how its any better than the steel work?

3. Where am I to buy one of them from? I do not know enough about transformers to even know if what I am buying is suitable in that respect, yes I know how they work, but have very little experience in using them and certainly not in this area.
 
Hi E54,

I don't make the rules lol

Option 2, using this method the additional rods need a low enough Ra as a standalone solution, you cannot rely or really take into account of any bonding connections as this could change and is outside of our control, in other words they have to be low enough Ra on their own to satisfy that exemption.

Option 3) Is valid according to the regs, whether that is a better solution is open to debate lol
 
1. I am just waiting for Amazon to deliver my book to day so will look at (i) then and calculate it.

2. I could put rods in, but what is it actually going to achieve on the basis the steel of the building is already doing the same job? I am not against the idea, but want a rock solid explanation as to how its any better than the steel work?

3. Where am I to buy one of them from? I do not know enough about transformers to even know if what I am buying is suitable in that respect, yes I know how they work, but have very little experience in using them and certainly not in this area.
tell me roughly where and ill look in mine and post a pic, just got mine 10mins ago
 
I didn't say it couldn't, but you have no idea of it's standing value at the moment do you??

No I don't, there is a brand new building going in next door to theirs which is identical so may take a look at it to see what the footings are like and how its anchored, might give me an insight.
 
Hi E54,

I don't make the rules lol

Option 2, using this method the additional rods need a low enough Ra as a standalone solution, you cannot rely or really take into account of any bonding connections as this could change and is outside of our control, in other words they have to be low enough Ra on their own to satisfy that exemption.

Option 3) Is valid according to the regs, whether that is a better solution is open to debate lol

Were talking about a steel structure with maybe piled steelwork and a foundation slab that has steel reinforcement, (which could also be tapped and connected to the buildings MET) what would you honestly expect to change?? The DNO's TN-S, TNC-S, PME earthing provisions are out of our control too. The only earthing system that would be under local control is a made electrode TT system....
 
Section 722.411 I think it was, then it refers to the an annex so you can calculate it something.
yeah section 722 is "Electrix vehicle charging installations"

10f5c300ff556eb6ecf547b8a6316496.jpg


83d824f18cd98caa6d60840b14726c4d.jpg
 
Were talking about a steel structure with maybe piled steelwork and a foundation slab that has steel reinforcement, (which could also be tapped and connected to the buildings MET) what would you honestly expect to change?? The DNO's TN-S, TNC-S, PME earthing provisions are out of our control too. The only earthing system that would be under local control is a made electrode TT system....

I accept that, but my argument is that the steel work is probably going to provide a better resistance than I will achieve with a load of rods.
 
Well at the moment we don't have any idea as to values, construction method or any other hard data, secondly the services could change (not likely on a new build I agree), there is a formula that needs to be calculated to see what value the Ra is required to meet that particular exemption, it takes no account of existing steelwork or services that may or may not be present.

He is the man signing the paperwork to say it complies and which exemption he is using.
 

Reply to Earthing for an EV Charging Point in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

Hi What the Maximum number of EV charge points that you can install in a Domestic system.
Replies
2
Views
212
A question perhaps for @Gavin John Hyde or others: I have a potential customer who is looking for an EV charge point installed at his property to...
Replies
7
Views
2K
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
3K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
519
Hi I currently have Megger MFT 1721, I am looking to buy the megger tester attachment for EV charging , does anyone knows if the MFT 1721 takes...
Replies
2
Views
826

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock