Hi guys
I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the other side of the warehouse. My question is does the pipe need to be bonded? Incoming metal gas pipe I believe is 28mm. Distance from that pipe to DB earth terminal is about 30m hence my question.
Thanks for any reply’sC9DA2F41-7CDC-4904-8203-1EF63096263A.jpeg
 
Last edited by a moderator:
Yes it does…. If it’s a metal incoming pipe, which it looks like.
Was it bonded before the DB was moved?

There will still be gas up to the meter, so it’s highly feasible that the building can still use gas… I’d say it’s still an active service.

A further question could be, do you equipotential bond between the gas pipe with its main bonding, and the structure… which will also have a main bond.
 
Yes it does…. If it’s a metal incoming pipe, which it looks like.
Was it bonded before the DB was moved?

There will still be gas up to the meter, so it’s highly feasible that the building can still use gas… I’d say it’s still an active service.

A further question could be, do you equipotential bond between the gas pipe with its main bonding, and the structure… which will also have a main bond.
It was bonded before but they strip all the cables when they refurbished. There is no outlet pipe from the meter. Shall I then clamp 60cm from of the meter on inlet metal pipe? Main earth in DB is 16mm so I guess I can run 10mm earth cable to bond that? They not going to use the gas as they have all electric now (heaters etc.)
 
Yes it does…. If it’s a metal incoming pipe, which it looks like.
Was it bonded before the DB was moved?

There will still be gas up to the meter, so it’s highly feasible that the building can still use gas… I’d say it’s still an active service.

A further question could be, do you equipotential bond between the gas pipe with its main bonding, and the structure… which will also have a main bond.

Hi guys
I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the other side of the warehouse. My question is does the pipe need to be bonded? Incoming metal gas pipe I believe is 28mm. Distance from that pipe to DB earth terminal is about 30m hence my question.
Thanks for any reply’sView attachment 107473

Hi guys
I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the other side of the warehouse. My question is does the pipe need to be bonded? Incoming metal gas pipe I believe is 28mm. Distance from that pipe to DB earth terminal is about 30m hence my question.
Thanks for any reply’sView attachment 107473
Unfortunately you do need to bond a metal gas pipe even if it's not used - unless you can prove with an insulation tester that it does not introduce earth potential into the property. (It probably does, but it looks like it may be ducted so who knows). Alternatively, you can permanently box it in with insulating material, if it can't be touched, there is no risk.
 

Reply to Earthing gas pipe warehouse in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K
A 'Sunday challenge' for the qualified electricians.... Can anyone explain why a built-in gas meter housing box that is located 600mm above a...
Replies
8
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock