My customer wants to have one ring main connected via a change over switch to a generator.
Earthing is TNCS
My idea was is move the ring main to a new consumer unit run a 6mm T&E to the change over switch from the 32 amp mcb in the main C/U where the ring main was. Then a 6mm T&E back from the change over switch to the new C/U.
I would install an earth rod which would be connected to the new C/U so the new C/U would have two earths one from the existing C/U and one from the earth rod.
The house is in a village with lots of overhead wires and I just thought what would happen if the neutral was brought down by a tractor then the return current that would normally go down the neutral of all of the houses after the break would be back fed through my customers C/U through the ring mains T&E and to ground via the earth rod. This could easily be a very high current which would surely melt the earth wires of the ring main.
Am I missing something ?
so you are using the earth separate ?
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.
now the I get the story.
it would flow down the neutral after the break into my customers house at which point the neutral and earth are linked together, then to the existing C/U then to the CPC of the ring which is linked to the earth rod.
Hope that make sense !
But that wouldn’t flow through the cpc of the ring circuit, it would flow via the earthing conductor and cpc to the changeover switch, then to the essential services CU, then to the earth electrode.
Whatever position the changeover switch is in, as you have described it, the route from the N-E link in the cutout to the earth electrode will always be via the 6mm T&E’s rather than via any final circuit.
Not applicable here, but on a larger standby set, where there is an N-E link, am I correct in thinking the generator earth should be connected to the MET of the installation? (as there will be times when both genset and DNO supplies are energised concurrently, e.g. after the DNO supply is restored following an outage, prior to the AMF changeover switch reverting to the DNO supply)
Reply to Earthing Generator TNCS in the UK Electrical Forum area at ElectriciansForums.net
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
How should grounding be made to a 20kVA single phase generator set feeding a domestic property via a manual change over switch? At the generator's...