Discuss Earthing of a conduit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi there I work in a shopping centre and the tills are supplied by a chrome pole ( non standard ) that comes from a metal burgess ceiling . Inside the pole is a 2.5mm 3 core flex and a CAT6 cable (non screened ) that supplies the till . This pole does not have any earth . I’m now being asked to use an earth clamp to connect the pole to a piece of trunking above the ceiling via a 4mm cable . Question 1 is this necessary? Question 2 should the earth from clamp be connected to the same earth that is contained in this pole ? And question 3 should the CAT6 cable be installed in same containment as the power supply ?
 
I would say (without reference to regs book)
Q1 - The metal pole should be bonded somehow - consider it as metal conduit / trunking
Q2 - more of a concern is that I would like to see the bonding connected to a bonding conductor ideally, not another item that is bonded.
Q3 - no, Band I and II cables shouldn't be contained together
 
I would say (without reference to regs book)
Q1 - The metal pole should be bonded somehow - consider it as metal conduit / trunking
Q2 - more of a concern is that I would like to see the bonding connected to a bonding conductor ideally, not another item that is bonded.
Q3 - no, Band I and II cables shouldn't be contained together
Thank you Tim these are what has been done already . I’m sure that this is wrong . Any regs references would be very helpful if possible too . E5DE41ED-0E19-487A-A9EB-A4FFCBD401D5.jpeg1F0337A2-7919-4011-8AD9-DDC6A736F240.jpeg
 
In no particular order, as I find them...
528.1 ....neither a voltage Band 1 nor a voltage Band II circuit shall be contained in the same wiring system....
(covering Q3, there is no question here, definite no no for data / alarm cables to be in same containment as supply cables)

411.4.2 ...exposed conductive parts of the installations shall be connected by a protective conductor to the main earthing terminal.
(It's clear the poles need earthing. 543.2 would allow the trunking to be used as a protective conductor assuming it is itself earthed. 544.2 confirms 4 sq mm is ok. So from what I can tell the method you have been using is probably ok)
 
Agree with above

Sounds like a DIY job on the pipe drop, those systems are probably expensive for the proper gear

Data and Mains cables in the same pipe and no connection tag
 
In no particular order, as I find them...
528.1 ....neither a voltage Band 1 nor a voltage Band II circuit shall be contained in the same wiring system....
(covering Q3, there is no question here, definite no no for data / alarm cables to be in same containment as supply cables)

411.4.2 ...exposed conductive parts of the installations shall be connected by a protective conductor to the main earthing terminal.
(It's clear the poles need earthing. 543.2 would allow the trunking to be used as a protective conductor assuming it is itself earthed. 544.2 confirms 4 sq mm is ok. So from what I can tell the method you have been using is probably ok)
Thanks Tim that really helps a lot . The only issue I thought with the trunking was that if the earth to the trunking was to be disconnected for whatever reason then it would lose its earth to the pole too .
 
[Devil's Advocate]
If the cable is 6491singles, insulation and no sheath, then the down pipe is acting as part of the electrical installation, is exposed, conductive and should be earthed.

However if the cable is 6492 or flex, insulated and sheathed, then the down pipe is simply cosmetic, not forming part of the electrical installation, just making the cable drop look pretty.

I'd argue it is not protecting the cable from likely mechanical damage (such as in a traffic area) in which case it is part of the electrical installation and would need earthing.

I know we all hate them but consider the "double insulated" class 2 metal light fittings that are not earthed yet are metal thus conductive but because the wires within are insulated and sheathed they are permitted, as are other similar class 2 metal bodied appliances.
[\Devil's Advocate]

The above assumes these poles aren't extraneous.

The data is a different matter, that's a definite no no, although ubiquitous.
 
If the cable is 6491singles, insulation and no sheath, then the down pipe is acting as part of the electrical installation, is exposed, conductive and should be earthed.

However if the cable is 6492 or flex, insulated and sheathed, then the down pipe is simply cosmetic, not forming part of the electrical installation, just making the cable drop look pretty.
I'm going to reflect on that while conceding you may be right! The definition of electrical installation is so broad in section 2...

Hypothetically if you had a run of steel trunking within a single room that only had T+E in it, would you not earth it then?

My thinking was whatever the cable is, extreme things like this can still happen (fresh in mind from video I posted earlier today) and earthing the pipes feels like a good plan.

1629312929531.png
 
[/QUOTE]
The flex is double insulated but could possibly be damaged going into the pole , and the cables are not screened cables so I think it’s not correct

That is an issue of good workpersonship.(?)

Even if we agree its a part of the electrical installation, any cables should be installed so as not to become damaged.

A coulper and brass brush on the top would solve that issue, earthing the pipe will not it merely mitigates the resultant consequences of the cable becoming damaged.
 
I was just going to say - I think if it was contained in something that was designed to hold electrical cables, and had provision for ensuring a non-sharp exit at the top e.g. a coupler and brass bush, it would be easier to say that's fine.
There is a reg saying enclosures should not have sharp edges. So something should be done about the top exit really. Even sitting a 25mm conduit box or elbow on top would improve matters!

I also think it's hard to prove from definitions in the regs whether they are exposed conductive parts or not, you might even argue that as they poke through a ceiling they are extraneous...

One thing is for sure - the money saving method of installation has spooked someone enough to commission this work!
 
My biggest concern is the newly installed power and data cables above the grid have no method of support that prevents collapse in fire.
 
My biggest concern is the newly installed power and data cables above the grid have no method of support that prevents collapse in fire.
I agree, there are multiple cables flying everywhere in this ceiling , no cable support whatsoever , no tray , no basket , not even cable tied up anywhere . Major fire hazard i think
 
That is an issue of good workpersonship.

God, give me strength. PC gone mad.
 
That is an issue of good workpersonship.

God, give me strength. PC gone mad.
You'll probably find that workpersonship is now verboten in favour of a term more inclusive of those that identify as unicorns.

PC is now not enough for the progressives, you'll have a trawl through the Guardian and find the latest approved term.
 
A coulper and brass brush on the top would solve that issue, earthing the pipe will not it merely mitigates the resultant consequences of the cable becoming damaged.
I'd settle for a female brass bush you could even add a lockring and banjo to give an earthing point
 
Is there a proprietary system for this ?

I know there is power poles and posts but this is basically a piece of containment or pipe

In theory it may not need earthing if a double insulated cable and grommets/bushings are used

But the above is ideal circumstances, it may be hazardous as described without the link to the steel trunking
 
You'll probably find that workpersonship is now verboten in favour of a term more inclusive of those that identify as unicorns.

PC is now not enough for the progressives, you'll have a trawl through the Guardian and find the latest approved term.
youcan't mention unicorns without mentioning unifannys.@ Ill get my coat.
 

Reply to Earthing of a conduit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
848
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
499
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock