advice needed please , what is the correct thing to do. The scenario:

-meter position and switch fuse @ front of house , with 100mA time delay protecting submain (TT SYSTEM)
-the above submain supplies a 17th ED split load DB at back of house (2 x 30mA rcds etc etc)
-submain is only 10mm T+E (4mm CPC within cable)
-@ the split load db it has 6mm cpc to earth rod close to this db (at back of house)
-should i connect 4mm cpc within twin and earth at switch fuse position to a 2nd rod via an addition 6mm earth?
(at front of house). ie front rod ---6mm---sw fuse ---4mm in T+E-----17ed db--------6mm-------back rod
-i believe the min for TT is 6mm and therefore the 4mm within the 10mm t+E submain throws me a little.
do i keep rods seperate, and only connect one of them to the sub main??

i guess ideal scenario would be to run an addition 6mm between db's or increase submain size, but this isn't viable really.
please can i have other opinions on his matter. thank you very much. ps new to this forum
merry xmas :)
 
earth rod should be at the origin of the supply so install new rod and connect it to switch fuse, then connect both rods together will give you a better overall Ra
 
Welcome to the forum.

The minimum size for a main earthing conductor (protected against damage and not buried) on a TT system is 2.5mm² (subject to complying with the adiabatic calculation).
Effectively you have your means of earthing connected to the origin by the submain.
There would be no problem with installing an extra rod at the front of the house and it could only reduce your Ra which would be good.
 
Makes a change to see an up front S type RCD backing up the 2 30mA units!!

Cable size connecting Earth electrodes to the MET are directly related to the Ra values obtained, the closer you get to 1 ohm or TN values the closer those main earthing cables need to be to match those required by TN-S. Not forgetting of course minimum requirements relating to method of installation as laid out in BS 7671....
 

Reply to Earthing on a domestic TT supply system with submain, advice needed please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
494
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
772
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock