Whats this.?.Cable on the left is alluminium, right one is copper. A couple of strands has been taken out from copper neutral and connected to outer pipe of left cable and then to main earth terminal. Is it tns,tncs,tt?,no earth electrode anywhere found
 

Attachments

  • 20200809_224752.jpg
    134.9 KB · Views: 46
Looks like a looped supply

And not a very good pme conversion connection from the original tns?
looks like a poor job

The original supply cable to the left then the right hand cable is obviously an addition

Is it in a house turned to a maisonettes/flats or something similiar

Whats your ze reading, doesnt look like tt
 
Last edited:
It's TNS
Cable of the left looks like Lead covered not alluminium.
Cable on the right looks like Split concentric with L and N linked inside the Cutout and the Earth linked at the original earth cable clamp.

As Welchyboy, right hand side is a looped supply
 
Whats this.?.Cable on the left is alluminium, right one is copper. A couple of strands has been taken out from copper neutral and connected to outer pipe of left cable and then to main earth terminal. Is it tns,tncs,tt?,no earth electrode anywhere found

It is a looped supply that has been added at a later date than the original supply.
Cable on the left is not aluminium, it is lead.
Cable on the right is split concentric.
A couple of strands have not been taken out of the neutral, the earth has been brought out of the bottom of the cutout and connected to the earth of the original cable.

Whilst it doesn't need an earth electrode there is a perfectly good one plainly visible there, the sheath of the lead cable.
[automerge]1598004182[/automerge]
And not a very good pme conversion connection from the original tns?
looks like a poor job

I can't see anything to suggest a conversion to PME, what makes you think that?
 

Reply to Earthing system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
So this is 1st floor maisonnette with concrete floor, 16mm2 single insulated tails coming from dual cut out on ground floor, through steel...
Replies
5
Views
845
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
521
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock