Discuss ECIR requested by the supplier. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have an EICR to do. The customer has said the electricity supplier were due to replace the meter but have not reconnected the installation until they get a 'certificate to say its safe'. They have said they only require dead tests to be preformed (obviously) and no inspection of accessories is required.
This has all been conveyed to me by the customer. So my question is should I just do the dead tests and nothing from the inspection schedule. And make this clear in the agreed limitations. (Again, it is the customer that has requested this, as advised by the electricity supplier)
Senarios...
I see no RCD protection and glance in the bathroom and there is no supp bonding?
I can clearly see that a radial in 2.5mm is protected by a 32A mcb?
I've not been to the property so this is hypothetical (until tomorrow). I was just drafting an email to the client setting out the limitations when I thought I'd seek advice from the masses.
You should conduct all the tests and inspections on the EICR except the live tests ........................ unless you agree limitations with the customer .............
I understand I should do everything that isn't included under 'agreed limitations' however what I'm saying is that the client is requesting just dead test be performed as per the instruction from the supplier. Therefore the inspection schedule would be a agreed limitation.
It would make the report extremely weak but it is a report based on the needs/requests of the client and the limitations (all of them) would be documented.
If that is the case (above), it doesn't quite seem right that it can be given satisfactory if I see (off the record) that there is a circuit incorrectly protected.
An EICR is a report on whether the installation is safe for continued use.
If you do not conduct an inspection, then you can’t really say that the installation is safe for continued use.
Reasonable limitations such as not lifting floor boards, or not conducting dead tests on certain circuits that need to be kept energised, is one thing.
A limitation not to even visually inspect the installation is a bit much, makes the EICR virtually worthless.
I would suggest you at the very least visually inspect the installation to look for glaring defects or dangerous conditions, then conduct the dead tests.
Then write a letter detailing what you have inspected and the test results, indicate whether in your opinion the installation is safe to be energised.
I would further suggest you query why the DNO are refusing to energise the installation and perhaps advise that a full inspection and testing is conducted after the installation is energised.
Dead tests will give you polarity, earth continuity of cpcs/ main protective bonds and insulation resistance and if these all prove to be satisfactory you have done what you have been asked to do. State the extent of the Report and fill it in accordingly.
I disagree. There is a box especially for detailing what the condition report is for. Put in there “to determine dead installation is safe to be made live by the DNO”.
This then spells out clearly what the report is for and would make it clear why the excessive limitations.
It would aslo make sure the report could not be misused by the owner.
My Area Engineer recommended also making a note in the EICR that live testing must be carried out upon re-energisation of the supply in order to verify that the installation is indeed in a satisfactory condition. (Obviously otherwise we don't even know if the RCDs operate correctly as an example.)
Not a bad shout.
Could also date the next inspection as the day the DNO energise.
If you look at the notes for EICRs on the model forms, it clearly states the report is to confirm where reasonably practicable that the installation is in a satisfactory condition for continued service.
If this inspection is to be conducted in accordance with BS7671, the very first thing to be done is to visually inspect the condition of all electrical equipment which is not concealed.
God forbid that after failing to spend 10/15 mins looking round the place and you sign off the installation as being safe to energise, that someone is electrocuted due to bare conductors hanging out of a wall or ceiling, or exposed by a broken socket front plate.
Seriously, are you not going to walk around and count points served, or confirm circuits?
Of course you would. In order to complete dead test you would dommost of that anyway.
Is that what is being debated?
Reply to ECIR requested by the supplier. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
4K
Next door neighbour .Single mother 2 young kids . Been there 6-7 years .landlady is super reluctant to ever communicate no matter what the issue ...