Just want to pick your brains.

When your completing the EIC on a consumer unit upgrade,what do you guys put on these parts of the schedule of inspections.

Section 8.3, 8.7.

My accessor said I should put “LIM”, but you can’t put “LIM” on a EIC! Obviously for section 8.7 you can’t possibly check ALL the cabling under floors, above ceilings or in walls etc.
 
N/A for cable routes supported through out and for cables In prescribed safe zones, after all we can’t verify what we can’t see and it’s not applicable to just a consumer unit change unless you have installed any cables as part of the extent of works covered by the certificate
 
I think NV or NA is fine and as Spin says, you are only responsible for what you are doing.
 
I using iCertifi which only allows you to put N/A or a ✔️.
 
Good point with the N/a Because to put NV as I suggested earlier would mean you had tried to verify it when in fact you didn't because you shouldn't because it not relevant to what you've done.
But that's easy for me to say :rolleyes::rolleyes:
 
Good point with the N/a Because to put NV as I suggested earlier would mean you had tried to verify it when in fact you didn't because you shouldn't because it not relevant to what you've done.
But that's easy for me to say :rolleyes::rolleyes:
Yeah I see what you mean. I will stop doing that as it is a bit confusing now I see it from the other side.
 

Reply to EIC completion on consumer unit upgrade in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
802
C
Hello, I recently bought and moved into my first home, and I made an enquiry with an electrician about doing a like for like swap of electric...
Replies
22
Views
3K
coalminers crufties
C
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hello, you all helped me out recently when we had a water leak (mostly in kitchen ceiling), and my landlord's contractor was saying the household...
Replies
7
Views
2K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock