that the designer and installer intend to comply fully with the requirements of BS 7671: 2018 (as amended). All new and rewired installations designed after 31st December 2018 are, without exception, required to comply fully with the requirements of the amended standard. Where exceptionally, after that date, designers and/or installers decide to adopt alternative approaches for alterations and additions to existing installations, they must be recorded as departures from the current standard in the box provided for the purpose on electrical installation certificates based on the model form given in the BS 7671: 2018 (as amended). Where such an alternative approach is taken, the designer and/or installer (as appropriate) must be prepared to justify the decision, and the resulting degree of safety of the installation must not be less than that obtained by compliance with the amended standard.
please in light us about the reg .
411.3.3 Additional Protection
In A.C. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for.
Socket-outlets with a rated current not exceeding 32 A, and
Mobile equipment with a current rating not exceeding 32 A for use outdoors.
And exception to (i) is permitted:
Where, other than for an installation in a dwelling, a documented risk assessment determines that the RCD protection is not necessary.
Reply to EIC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Is it acceptable to lim on eic for supply characteristics? I had a job in a hospital today and I couldnt gain access to the Switch room and the...
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
6K
I've just started using the NAPIT forms for EIC's and EICR's and they are a bit cumbersome to be fair. Does anyone know which observation is for a...