Hi just carried out an EICR prior to a consumer unit change. The customer has a wet room with a normal baton type accessorie. The ceiling height is more than 2.25 mtrs but the shower head is less than 1.2 meters from the light in a straight line. There is no rcd at the minute but will be once the new board is fitted. I will put that as a code 2 but will the light be ok once its rcd protected. my commoon sense thinks its not ok but the ceiling height is out of zone 1 ?
 
that's a C2 IMO. fitting is not suitable for location. exposed lamp could shatter causing injury to anyone in the shower. also water ingress could cause problems.
 
Zones aside, the fitting has to be suitable for location, the location being a wet room.
In my opinion, it's not suitable for location in this instance and I would also opt for a C2.
At the end of the day, it's your opinion that matters as the inspector signing the EICR.
 
C3 for no rcd for bathroom light.
C2 for unsuitable light fitting if within zones
C3 for unsuitable light fitting if outside zones

Dunno why but i always enjoy the PIR code questions :-D i'm weird lol.
 
Zones aside, the fitting has to be suitable for location, the location being a wet room.
In my opinion, it's not suitable for location in this instance and I would also opt for a C2.
At the end of the day, it's your opinion that matters as the inspector signing the EICR.

Thanks for all your opinions & help on this. Will recommend the light is changed. Will put my mind at rest. Everything will be RCD protected now anyway.
 

Reply to EICR Code for wet room light in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
670
I wonder if you can help I've just had a EICR on a property and I've received a C2 due to the fact the down-lights aren't IP rated. Having sat the...
Replies
18
Views
3K
I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet...
Replies
31
Views
3K
I've purchased Lepro 15m LED strip lights - product code PR410047-RGB-UK, and have fitted them at the top of the walls in my daughter's bedroom...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock