Just done a EICR and have found on one of the 3 phase DB's that most of the neutrals and cpcs on one side of the DB are all mixed up and not in correct terminals. To rectify needs a few hours to strip it all back and re terminate due to how messy it has become over the years with add on's etc so I have not done it as part of the reporting process.
I believe this is a code but am a little unsure between C2 or C3.

Thoughts please would be greatly appreciated?
 
if you were to disconnect the wrong neutral while working in there, you could easily get a belt off it through the load which is still energised deffo a C2 IMO.
 
A 3 probably, a rough Job, but it would be difficult to code it 2 even though it probably could be a 2, how do you argue this with the customer and look right? have to have a good think over this, a toughy for a 2 IMO.
 
Yeah i'm tied between the 2 and 3 at the moment. Swinging more to the 2 as well put by telectrix, defo POTENTIALLY DANGEROUS although can see Mikes point about justifying it.
On the basis of the wording of the codes i.e 'C2 potentially dangerous' gona have to go with the C2 I think!? ;-/
 
I expect your right tel with the code 2, just wondering how to convince the customer it is actually dangerous that was my only point.
 
A C3 at most. Most competent electricians would check before removing the neutrals. Recommend within your summary, that a suitable label be fitted highlighting the conductors are not suitably arranged.
 
and if the cables are singles, how in hell can a spark know which is which. if he disses the wrong one, he's got a live cable in his hand and it could potentially cause a danger by suddenly switching off a circuit in use.
 
I was in doubt but defo a C2 for me now on reflection. The cables in question are singles and as well described by Telectrix it is potentially dangerous, which is the desciption for a C2. A single phase CU on the same job was the same but not so messy and the cables were easily identifiable as T&E so as I tested through the CU it was easy to rectify as part of the process.
If this 3 phase wasn't so messy I would do the same but due to the mess off it there's a few hours works disconnecting, sorting out & reconnecting which is not in my quote for the EICR.
 
and if the cables are singles, how in hell can a spark know which is which. if he disses the wrong one, he's got a live cable in his hand and it could potentially cause a danger by suddenly switching off a circuit in use.
Technically he shouldnt be working on a live CU should he?.After all even if neutrals are in correct order it's very hard in a cramped space to be sure you've got the right one. Board should be isolated before disconnecting cables.....code 3 for me.
 
and what if the board is in use running machines on a production line and you are required only to decommission 1 circuit. you won't be flavour of the month.
 
How does he tell? Well I'm sure that a single clamp meter would solve that problem. Besides if the op noticed that the arrangement was incorrect, then other competent persons should also.
Just because its singles, would you remove a neutral just because it looked right? Even if it was marked?. No chance
 



C3 ... You should be double checking before working on the circuit ... All in my opinion of course



That's a fair enough opinion,but

Real world economics will over ride all the safety regs that could be mustered against that procedure

Yes,the board should be isolated,but reality as opposed to text book procedure will ensure that it's a bigger danger than it needs to be

Code it reality or code it text book,mmmm

Code 3
 
Last edited:
In order to code it has to not comply with 7671.....while no doubt a reg concerning ID of circuit conductors could be found,if a sparks was electrocuted disconnecting an energised conductor in a CU I have absolutely no doubt that an inquest would find him breaking H&S rules by not isolating first
 
C3 for me it's only potentially dangerous if working on the board live, as it's already been identified by yourself and like someone has said mark up the board for future sparks stating that the "neutrals are not connected correctly, de-energise board before removing cover" Having said that if it was a new job I'd sack the spark for doing a rough job.
 
I agree with kas1 code 3 all day long it not dangerous to general public or people working their only someone working on the electrics and well they should be competent so if they got a belt then they aint competent.
 
name me 1 spark that has never had a shock of some sort in their working life.
 

Reply to EICR code thoughts please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
513
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
597
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
635

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock