Hi,

What code would people put for a lighting cable going along skirting board with no trunking ect, its in a really old building so not sure weather this complied then or not as its in an exposed position, i want to put c2
But is it c3

Would be thankful for your input

Regards Kurtis Randle
 
C3, unless there's signs of damage or an obvious specific risk. After all, you'll find loads of flexible cable lying around on the floor of most properties and that generally survives.
 
C3 states improvement recommended , and as i would not install clipped direct in a vulnerable position unless mechanically protected eg trunking ect
More common sense, there is a reg stating any cable clipped direct must be mechanically protected unless in a non vulnerable position, not 100% sure where or how its worded but i have seen it, i will take a look later
 
Last edited by a moderator:
C3 states improvement recommended , and as i would not install clipped direct in a vulnerable position unless mechanically protected eg trunking ect
More common sense, there is a reg stating any cable clipped direct must be mechanically protected unless in a non vulnerable position, not 100% sure where but i have seen it, i will take a look later

Then you need to be quoting that reg if you feel it is appropriate to the installation. For your reference it is reg 522.6.1.
Remember that an EICR is a report based on BS7671 and any coding must be able to be justified with a regulation. Your personal opinion and common sense is not a part of BS7671 so has no place in the report. You need to keep this in mind to save yourself from producing potentially fraudulent documents, especially if you are quoting for remedial work on the back of your report.
 
Fair play, what i meant though was common sense normally falls into a reg anyhow if that makes sense. Cheers i will have a look now

Yeah you are right, but there a few instances where the regulations do not fall into line with what we expect. Remember that BS7671 is a minimum standard and sometimes not up to our personal standards, but only the minimum standard applies to the report.
 
C3 states improvement recommended , and as i would not install clipped direct in a vulnerable position unless mechanically protected eg trunking ect
More common sense, there is a reg stating any cable clipped direct must be mechanically protected unless in a non vulnerable position, not 100% sure where or how its worded but i have seen it, i will take a look later

Just because you would not install it that way doesn't necessarily mean it is wrong.
What do you perceive this T&E to be vulnerable to? Are there any signs of damage? If it has been there for a number of years and not suffered yet I would say that it's not particularly vulnerable. Especially considering that older T&E is a damn sight tougher than modern stuff
 

Reply to Eicr codeing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
671
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
953
Ive been asked to quote for remedial work for local village hall after another company flagged up some C2's along with C3's The C2's are...
Replies
3
Views
1K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock