How would you code a bathroom with all insulated fittings , no supplementary bonding and not supplied by rcd .
The old BPG4 seemed to suggest its not required to report ,but it no longer states this in the latest BPG4
 
all pipework was copper as observed and would be connected via the boiler , via the gas and water both which have 10mm bonding.
at one point i used to code these as C2 but im struggling to find any danger from a pullcord and a ip65 rated class 2 fiting on the celing.
 
all pipework was copper as observed and would be connected via the boiler , via the gas and water both which have 10mm bonding.
at one point i used to code these as C2 but im struggling to find any danger from a pullcord and a ip65 rated class 2 fiting on the celing.
Ah ok.But if the piping has insulated sections between these points or before all accessible pipework in the bathroom they wouldn't have continuity and if it was insulated inside the bathroom before accessibility they wouldn't necessarily be extraneous. But I'm sure that's been checked. Also if none of the above applied but the continuity between the cpc of the fittings and the extraneous conductive parts had a low enough impedance to allow the protective device to disconnect in the correct time , then it could be assumed that there is supplementary bonding, just a thought.
 
I think this is technically a C3 where simultaneously accessible (701.415.2 does mention class II's), but I doubt I'd code it as I probably wouldn't be looking for it as part of an EICR. Like you say, it's hard to see what danger it poses in its current state.
 

Reply to eicr coding (bathroom) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
490
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
770
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock