Discuss EICR coding (C1,C2,C3,N/A) in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

gazdkw82

-
Arms
Reaction score
739
Just doing some mock exams for the upcoming 2391 course.

Confused on this question as I got it wrong.

Q. If a lighting circuit installed in metal conduit in a shop supplied from a TNS system had no RCD provided for fault protection but achieved disconnection times what would the outcome be on the schedule of inspections.

I put it as a C3. Improveme needed.

The answer has come back as N/A.

Can any explain this?
 
Yes.
There is no requirement yet to provide RCD protection for lighting circuits.
The lights themselves do not require RCD protection, and the cables are contained in metal conduit which provides protection from nails and screws.

Ah (silly sod) because I've been studying the 18th I've convinced myself that rcd on lighting circuits is a requirement.
 
Yes.

Why?

Not enough info in my opinion.

No mention in if the conduit is earthed.

No mention on if it is surface of chased in the wall.

Assuming it is earthed then no code. If it is not earthed then C2 for no earth and if it is chased in the wall with no earth then a C3 for no RCD also.
 
Not enough info in my opinion.

No mention in if the conduit is earthed.

No mention on if it is surface of chased in the wall.

Assuming it is earthed then no code. If it is not earthed then C2 for no earth and if it is chased in the wall with no earth then a C3 for no RCD also.

Yeh I agree
 
Yes the question is a bit confusing its trying to dissect what they are getting out , For example what part of the schedule are they referring to

RCD(s) provided for additional protection, where required - includes RCBOs (411.3.3; 415.1) then N/A

Adequacy of protective devices: type and rated current for fault protection (411.3) then it would be Pass​
 
Doesn’t matter if it’s earthed.
Doesn’t matter if it’s surface or concealed.
Only thing that would mean RCD protection is required, is if it’s part of a circuit of a location containing a bath or shower.
It’s a shop, so that is unlikely.
I thought if your using conduit as mechanical protection it had to be earthed , or does it not because conduit will prevent a screw or nail from Penetration , ( Now there a word for a Friday afternoon :))
 
I thought if your using conduit as mechanical protection it had to be earthed , or does it not because conduit will prevent a screw or nail from Penetration , ( Now there a word for a Friday afternoon :))
The options for providing additional protection for cables concealed in walls are:
to bury the cables at a depth greater than 50mm,
to use a cable with an earthed screen,
to use earthed conduit or trunking,
to provide mechanical protection sufficient to prevent penetration by screws and nails,
to run the cables in prescribed routes and provide RCD protection.
 
The options for providing additional protection for cables concealed in walls are:
to bury the cables at a depth greater than 50mm,
to use a cable with an earthed screen,
to use earthed conduit or trunking,
to provide mechanical protection sufficient to prevent penetration by screws and nails,
to run the cables in prescribed routes and provide RCD protection.
Ok so it has to in an EARTHED conduit system. So conduit must be EARHED
Unless the conduit is sufficient to protection to prevent penestration by screw or nail. Then NO EARTH is required.
Now I would of said that all the metal conduit I have used would stop a screw or nail but is there any metal conduit that could be penertrated?
I
 
Ok so it has to in an EARTHED conduit system. So conduit must be EARHED
Unless the conduit is sufficient to protection to prevent penestration by screw or nail. Then NO EARTH is required.
Now I would of said that all the metal conduit I have used would stop a screw or nail but is there any metal conduit that could be penertrated?
I
I have seen some very thin walled conduit whilst working on older installations. Sort of stuff you could literally squash with your fingers.
Nowadays I think light gauge conduit is something only found in places like the USA and Canada, or in the UK when it’s Stainless Steel.
The Galv steel conduit I use has a wall thickness of 3mm, though I understand it is possible to obtain a thickness of only 2mm.
Of course, there is flexible steel conduit (kopex), but that would only be suitable for use at a depth greater than 50mm, or within prescribed routes along with RCD protection.

Upon reflection, the question is probably based on the 18th edition, as it makes reference to ‘circuit’ and goes on to say the installation is non-domestic.
At present, the only circuits which require RCD protection, are those referenced in Part 7 Special locations.
Circuits of a location containing a bath or shower, etc.
 

Reply to EICR coding (C1,C2,C3,N/A) in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I’ve just done an EICR on an old 2 bed flat that is wired in all metal conduit wired in singles however there are no CPC’s. The conduits are all...
Replies
10
Views
3K
Hi all, we got an EICR report done before tenanting our previous home having become "accidental landlords". See attached. The report came back...
Replies
12
Views
4K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
On a test & inspection today, I came across an older Wylex split load board that had been modified to add RCD protection for all circuits (see...
Replies
6
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock