Certainly no code should be attributed to that. Conduit can be used as cpc so long as it tests out and shows no signs of corrosion or damp penetration.
20mm /25mm conduit tends to be the norm on domestic lighting so is ok normally.
Would only need to do this if the conduit is not suitable as a cpc which doesn't seem to be the casei think you might need to put a sticker on the DB warning the user not to change fittings to class 1 in the future and an observation on the sheet to the same effect
i think you might need to put a sticker on the DB warning the user not to change fittings to class 1 in the future and an observation on the sheet to the same effect