Testing on a commercial site which has an outdoor panel which feeds various car chargers and lighting, now upon opening the panel with a triangle key you have access to all switch gear now would you code anything for no secondary barrier? I opened another box and it had a plastic face plate?
Only asking as me and another lad have different views
 
problem is that everyman and his dog has a triangle key. a more secure keyand lock would be my answer, so that only authorised persons could gain access.
 
If you can see any plastic covers are missing, that the manufacturer would have fitted, then I would mark it as a C3, but if it was built without any could put it down as an FI, then you could look to see if you were able to install any, otherwise I would not mark it down, like others have said, if you need a key or tool to gain entrance, then it is not a fault.
 
If you can see any plastic covers are missing, that the manufacturer would have fitted, then I would mark it as a C3, but if it was built without any could put it down as an FI, then you could look to see if you were able to install any, otherwise I would not mark it down, like others have said, if you need a key or tool to gain entrance, then it is not a fault.
FI whilst you find out if it's a C3 or no code ? So unsatisfactory report whilst you investigate in which one of two ways it is satisfactory ?
 
C3 and FI don’t make it an unsatisfactory report, if that was the case, every install that was not installed under 18th edition would be unsatisfactory, you can put FI, and go away and look into it, just make a note, in the report, and put a covering letter with the report, when giving it to the customer,
 
C3 and FI don’t make it an unsatisfactory report, if that was the case, every install that was not installed under 18th edition would be unsatisfactory, you can put FI, and go away and look into it, just make a note, in the report, and put a covering letter with the report, when giving it to the customer,
A FI code will result in an unsatisfactory report.
You can’t give an FI code and deem it satisfactory
 
My NIC software with built in faults with codes lists old colour wiring as a FI......

That must be a bug in the software, there's obviously nothing to investigate when you can see clearly what colour the cables are.
[automerge]1572827908[/automerge]
C3 and FI don’t make it an unsatisfactory report, if that was the case, every install that was not installed under 18th edition would be unsatisfactory, you can put FI, and go away and look into it, just make a note, in the report, and put a covering letter with the report, when giving it to the customer,

FI does make it unsatisfactory, if something requires further investigation then it cannot be satisfactory.
If it was satisfactory then it wouldn't need to be investigated.

No, not every install which was carried out to a previous edition will have anything requiring further investigation.
[automerge]1572828049[/automerge]
problem is that everyman and his dog has a triangle key. a more secure keyand lock would be my answer, so that only authorised persons could gain access.

Screwdrivers are even more common than triangle keys yet screws are still acceptable to secure a cover over live parts.
 
C3 and FI don’t make it an unsatisfactory report, if that was the case, every install that was not installed under 18th edition would be unsatisfactory, you can put FI, and go away and look into it, just make a note, in the report, and put a covering letter with the report, when giving it to the customer,
What happened to the disagree button?
 
I had the same question about those little Russian dolls.
 

Reply to EICR coding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm having a bit of a brain fog moment (changing medication is such good fun!) and am looking for confirmation that I'm either right or talking...
Replies
3
Views
930
Hi guys I have been tasked with upgrading some old rewireable fuseboards for a food warehouse that runs continually 24/7. I was asked to do an...
Replies
10
Views
2K
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K
Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
Replies
1
Views
4K
Next door neighbour .Single mother 2 young kids . Been there 6-7 years .landlady is super reluctant to ever communicate no matter what the issue ...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock