I need a hand to confirm what coding goes with what please on this house

I have been asked to inspect a house by an agent and this is the situation:
  • TN-S Earthing (0.4 ohms)
  • No CPC in lighting circuit with Class 1 fittings
  • No Bonding to Gas or Water
  • No Sleaving on any CPCs
  • All CPCs twisted together and put into 1 conductor on MET (in CU)
  • Main Earth has been extended using a 6mm black (neutral) cable
  • 10 Sockets on a 20A Radial (2.5 T&E)
  • CU inaccessible under Stairs
  • RCD as main switch (only 5 circuits)
  • Trunking Missing exposing unsupported Cables
  • Extractor Fan in bathroom controlled by the shower circuit (no shower) on 6mm T&E 32A MCB
  • No labels on CU apart from an old damaged RCD label (this circuit or part of it is protected by an RCD)
  • Half a socket in the kitchen does not work (245v LE, 110v LN, 110v NE)

Rewire was done about 1 year ago in old (Red & Black) cables, not notified, no certificate - landlord said the electrician and gas fitter walked off site due to payment problems (not a clue)
Boiler is less than 1 year old - never been serviced or when it was installed

I know a few of these are not a cause for concern but they are there to draw the picture


Thanks for your help
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
S

sparks1973

  • Thread Starter Thread Starter
  • #4
well:
1) no code...as its within for a TN-S (0.8)
2)to me its a 1...get them class 1s dropped
3) a 2....will need bonding installed to services
4)well you could give it a 3...identification of conductors
5)again a 3...requires improvement..CPCs should follow the number of circuit they belong to
6) a 3...undersized CSA...wrong colour (identification)...i dont like the idea of a joint in it (i assume it isnt going into an earth marshalling block...well, its just wrong isn`t it..
7)give it a 3....the cables CCC is capable of carrying the max let though....but i would definately be inspecting these....
8)a 3..
9)go for a 3 on this....
10)unsupported cables....poss a 3
11)if not on an FCU...then a 2...this would be a fire risk....
12)a 3 here....no identification of circuits
13)..go for a 3 initially...but upon investigation be prepared for a 1..
 
Last edited by a moderator:
S

sparks1973

  • Thread Starter Thread Starter
  • #7
i think though where coding is concerned...its at the discression of the inspector & tester..(within reason)....
 

spark 68

-
Arms
Esteemed
I will have a go

have been asked to inspect a house by an agent and this is the situation:

  • TN-S Earthing (0.4 ohms) No code as it is within 0.8
  • No CPC in lighting circuit with Class 1 fittings, C2
  • No Bonding to Gas or Water, C2
  • No Sleaving on any CPCs, No code, or C3 as it may have complied at time
  • All CPCs twisted together and put into 1 conductor on MET (in CU) C3
  • Main Earth has been extended using a 6mm black (neutral) cable C3 or C2 depending on how it is joined
  • 10 Sockets on a 20A Radial (2.5 T&E) No code
  • CU inaccessible under Stairs maybe no code, as I cannot see the circumstances, possibly C2 or C3
  • RCD as main switch (only 5 circuits) C3, may have complied at the time
  • Trunking Missing exposing unsupported Cables, depends if T&E no code or C3, or singles C2
  • Extractor Fan in bathroom controlled by the shower circuit (no shower) on 6mm T&E 32A MCB, C2, incorrect OCPD
  • No labels on CU apart from an old damaged RCD label (this circuit or part of it is protected by an RCD) C3
  • Half a socket in the kitchen does not work (245v LE, 110v LN, 110v NE) needs further investigation, possibly C1 or C2 depending on the outcome of the investigation
I have ignored the part about being rewired a year ago, as this is hearsay as far as the EICR is concerned

obviously this is just a guess as this is on a forum, and Iam not on the ground
 
S

Silly Sausage

  • Thread Starter Thread Starter
  • #9
CU inaccessible under Stairs maybe no code, as I cannot see the circumstances, possibly C2 or C3

I think I'd give that a C2.
In the event of a fire, isn't that one of the first things they (Firemen) do, try and turn the electric off?
 

spark 68

-
Arms
Esteemed

I think I'd give that a C2.
In the event of a fire, isn't that one of the first things they (Firemen) do, try and turn the electric off?
It depends on the circumstances Archy, for instance if it is just obscured by junk then possibly no code or a C3, and just a word of advice, on the other hand if it truly is inaccessible or partially boxed in or similar then a C2.
 
S

sparks1973

  • Thread Starter Thread Starter
  • #11
i mean i looked at the fan thing from a slightly different angle......that is to say the cable`s Iz was adequate for the In....but it was the absence of local fusing down that concerned me most....agreed though it could/should have been done at source...
similar outcome though to 68`s....so just goes to show you can gain much info from a previous written report (if done correctly)....without actually being at site....
 
The agent can't really call it a 'Rewire' can they with out bonding and cpc's in lighting circuits along with everything else.......sounds like existing with a new rcd board change to me....u never know u might get to rewire the so called rewire,and these people will know not to get a gas fitter to mess with the electric, clues in the job title, GAS fitter lol.
 
D

Deleted member 26818

  • Thread Starter Thread Starter
  • #13
About the only time the 4Ω on a TN system would be a problem, is if the supply was 100A or above
 
G

Guest55

  • Thread Starter Thread Starter
  • #14
Life would be alot easier if you did some research yourself to further your own understanding.
The problem with coding is thats its entirely subjective , so as the person signing the report it has to be in your opinion.
With just a couple of items i'd help you out , but i cant be arsed going through over a dozen.
 
S

Silly Sausage

  • Thread Starter Thread Starter
  • #15
Life would be a lot easier if you did some research yourself to further your own understanding.
The problem with coding is that it's entirely subjective , so as the person signing the report it has to be in your opinion.
With just a couple of items i'd help you out , but i cant be arsed going through over a dozen.
Haha...I was thinking the very same earlier today.
You'd think it would be purely objective, which I suppose it mostly is, but surprising how much isn't.

(I always have to think about which is which with those terms!:confused::dunce2: )
 
S

SirKit Breaker

  • Thread Starter Thread Starter
  • #17
Biff as usual hits the nail on the head.

These things are subjective, but as you are doing the EICR, then you must have a good idea about what you are doing, and as such, you need to put your own professional comments on the situation.

For each problem, ask yourself the following.
1, Does it pose an immediate danger, if yes, then code 1.
2, Is it likely to cause a danger, if yes, then code 2
3, Does it need improvement, if yes, then code 3.
4, Does it comply to an earlier version of BS7671, but without faults, if yes, then code 3.

Without me seeing the install, then my opinion is based on the info you give, and you have something that falls into all of the above.

And by the way, just because it doesnt comply to 17th edition, does not deem it unsafe.

Cheers................Howard
 
G

Guest123

  • Thread Starter Thread Starter
  • #18
I need a hand to confirm what coding goes with what please on this house

I have been asked to inspect a house by an agent and this is the situation:
  • TN-S Earthing (0.4 ohms) No code.
  • No CPC in lighting circuit with Class 1 fittings C2
  • No Bonding to Gas or Water C2
  • No Sleaving on any CPCs C3
  • All CPCs twisted together and put into 1 conductor on MET (in CU) C3
  • Main Earth has been extended using a 6mm black (neutral) cable C3
  • 10 Sockets on a 20A Radial (2.5 T&E) No code
  • CU inaccessible under Stairs Define inaccessible.....
  • RCD as main switch (only 5 circuits) Whilst it maybe a pain under fault conditions, cant really assign a code to IMO.
  • Trunking Missing exposing unsupported Cables Definne unsupported
  • Extractor Fan in bathroom controlled by the shower circuit (no shower) on 6mm T&E 32A MCB More info needed
  • No labels on CU apart from an old damaged RCD label (this circuit or part of it is protected by an RCD) C3
  • Half a socket in the kitchen does not work (245v LE, 110v LN, 110v NE) Neutral issue, C2.

Rewire was done about 1 year ago in old (Red & Black) cables, not notified, no certificate - landlord said the electrician and gas fitter walked off site due to payment problems (not a clue)
Boiler is less than 1 year old - never been serviced or when it was installed

I know a few of these are not a cause for concern but they are there to draw the picture


Thanks for your help

I'll humour you with my own views.

If I was there, on the day, there maybe some variances in the above depending on what sort of 'feel' I got for the install.
 
erm... is it me?, the first question about TN-S is a the sort of question an apprentice might ask, have you not heard of guidance note 3
 
G

Guest123

  • Thread Starter Thread Starter
  • #21
Oi, Johnny 2 threads, I've just found this after answering your other identical thread.

Keep to one thread on the same subject please.

:icon6:
 
G

Guest55

  • Thread Starter Thread Starter
  • #22
Rewire was done about 1 year ago in old (Red & Black) cables, not notified, no certificate.
Something else puzzled me about this thread - the above comment.
Getting hold of enough old colour cable of the right sizes to do a full rewire is no mean feat , it will certainly be more cost and time consuming and its unlikely a couple of chancers will go to the trouble of getting it.
So i would assume no rewire was done at all to be honest , considering all the wiring faults and non-payment issues.
 
S

Spazz

  • Thread Starter Thread Starter
  • #24
This house is one I have just moved into with my kids and misses, agent just took it on and as I was looking he gave it to me to live in and correct anything and everything that is of concern

The situation is that the landlord refused to pay the sparky & gas man so they walked off site and didn't notify/finish anything!
Clearly from what I have seen here no work was carried out at all on the electric side anyway!



Lenny delete the other thread please.
 
S

Spazz

  • Thread Starter Thread Starter
  • #25
In regards to inaccessible CU the gap under the stairs is only 2 foot high and you have to be on your bell to get to the CU, the head and meter is under there as well as the gas mains and meter.

completely stupid place to put the utility supplies if you ask me!
 
G

Guest123

  • Thread Starter Thread Starter
  • #26
I'm not deleting the other thread as members have taken their time to post replies for you in it.

I'll merge the 2 so you have the benefit of both sets of replies.
 
S

sparks1973

  • Thread Starter Thread Starter
  • #27
In regards to inaccessible CU the gap under the stairs is only 2 foot high and you have to be on your bell to get to the CU, the head and meter is under there as well as the gas mains and meter.

completely stupid place to put the utility supplies if you ask me!
nick...this is nowt uncommon fella...CUs ,service heads n gas in thick places......had old BS3036s under sinks in the corner of the cupboard a few times......CUs where they`v been `boxed in` to (make em look neater?)...except you cant get the front of......it just goes on and on....if in doubt..just blame a kitchen fitter...its always their fault..lol...
 

Reply to EICR Coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net