EICR of a semi detached house. Wiring approx 20 years and in flat twin & earth.

I have found the following condition;- cpc's present but not connected at down lights on Downstairs lighting circuit. Joint box method and has been established there is an earth to JB. Down lights and other circuit accessories are all class 2.

What code would this observation warrant?

Cheers
 
A

aes2011

  • Thread Starter Thread Starter
  • #3
Ok, am I right in saying there should be a label fitted at DB warning occupants not to fit class 1 equipment?
 

telectrix

-
Mentor
Arms
Esteemed
no, because that only applies if the circuit has no cpc. in this case the cpc is present at the JBs and so could be connected to any class I fittings. i assume that all switchesw have a cpc to the back box ( and faceplate if metal)
 

Reply to EICR-down lights cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Thread starter Similar threads Forum Replies Date
Baddegg Electrical Forum 23
S Electrical Forum 11
S Electrical Forum 15
C Electrical Forum 19
M Electrical Forum 6
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Top Bottom