Discuss EICR Help! in the UK Electrical Forum area at ElectriciansForums.net
dlt27
Hi all, Any avice on the following would be appreciated.
The buildng is a listed building that has been converted into 4 flats. All flats have KMF with 16mm t+e to each flat fed from cupboad outide bulding. Gas meters are in the cupboard as well.(PME system)
1 what I would like to know is does each flat need to have 10mm bonds from outside MET to each flat as earth in t+e is only 6mm or could I use the adiabatic equation? (nightmare to do, each flats exising bonds are 6mm). Gas meters could be bonded in cupboard outside by MET, however i thought gas and water should be bonded where it enters each flat.
2 The one flat wants a board change done however DB is a foot above the floor. Is it ok to do this or would I need to raise it and do joints with adaptable box and din rail. (client wants new one put where exiting one is).
3 One flat has antique brass fittings with no earth terminal provided. Does anyone know if you can solder a terminal onto brass so I can earth them or is it new fittings?
4 What code would you give to 12v downlights in zone 1 and not IP 44 rated?
Thanks again for advice.
You need to bond the gas within 600mm of meter, yes the bonding needs to be 10mm and you cant use the adiabatic equation due to it being tncs (pme). The water will need to 10mm and you will have to run a bond upto the flats or at least to pipe that feeds that flat, are they not all metered somewhere before the flats ? if so you could bond them within 600mm of meter
The consumer is fine
you could solder it on and as long as its a good joint then no problem, are you sure it isn't a class II fitting because I got one recently and it had metal parts but didn't need earthing as stated in the instructions.
The 12volt downlights don't require a code as they are not 230v
No you do not need to run a 10mm cable from the Flat CU to the incoming services. It is a sub-main, so the bonding should be done at the Incoming service/ryefield board etc.
If you wanted to, you could bond the incoming services on entry to the flat.
It's an existing CU, so yes, you can replace it as it is now - make a note on the install Cert to state what you've done.
Yes, new fittings. Would you really be able to say you've reached the Product Standard when soldering on an earth tag?
Are the lights suitable for the environment? If they let water in, then they are not, even if they are 12 volts.
What do you mean if you wanted to? Services need bidding at the point of entry to each installation. Where multiple flats in a single building are concerned then bonding is required at the point of entry to each flat as each flat ha sits own electrical installation.
GN8 has some good diagrams which illustrate this perfectly if you don't understand
Providing the OP has as much common sense and tool using ability as a monkey then why shouldn't he connect an earth wire using a soldered joint?
3:
I know I can solder a terminal onto the brass plate using a silver solder to achieve a good performance at the maximum conductor operating temperature, but the question really is can you?
4:
I don't know the answer as you haven't given enough information! Is it an SELV supply or otherwise? For a start
Reply to EICR Help! in the UK Electrical Forum area at ElectriciansForums.net
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Hi All 3rd floor flat has incoming supply via Conduit which was being used as the earth. Conduit at some stage has failed leaving the property...
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...