eckersecker
Doing an EICR on the village hall. Red phase supplies a board that has sockets, fans etc on it and is supplied via a 30mA RCd. Blue phase supplies a board that has mainly lights on it but one breaker to a steel water heater type tea urn in the kitchen area. This is wired in via flex to a rotary isolator on the wall.
Although technically not a socket outlet am I correct in assuming it is treated the same way and is a code 3 , "Absence of RCD for a socket outlet...." or do I up it to a code 2 because it involves the use of water is also near a sink and could be considered a potential danger.
Although technically not a socket outlet am I correct in assuming it is treated the same way and is a code 3 , "Absence of RCD for a socket outlet...." or do I up it to a code 2 because it involves the use of water is also near a sink and could be considered a potential danger.