oracle

-
Esteemed
Arms
Reaction score
380
Here's one I wasn't expecting on an EICR. Recently rewired and renovated 2-bed property (2015ish). Having an EICR as a new tenant to move in soon. No reported problems.

I expected to be in and out in about 3-4 hours to be honest, and as expected I found nothing wrong until I began my ring final tests. All the sockets had already tested fine during my visual check and quick test with my Kewtech tester. I was a little surprised to find this property only had the one ring with the combi boiler also hanging off it, given the board was a 10-way with 4 spare ways in it. Made me wonder why during the rewire the property wasn't split into an upstairs and downstairs ring, but anyway....

So, RN tested out fine, but R1 - open circuit, R2 - open circuit ! Oh joy. At this point the current tenant piped up and said "Should I have mentioned some of the sockets were getting hot ?!"

Anyway according to the Codebreakers guide I should be giving this a C2 (Actually I'm thinking of giving it an FI), and handing the report to the landlord. I admit I don't get many outright failures, but this one obviously is.

Anyway what I was going to ask is I'm assuming what I have here is a ring that's functioning as 2 overloaded radials, and somewhere both conductors have a break in them (It'll be just my luck that they will be in different locations). It can't be classed a C1 can it, as this fault could have been there for years, and another couple of days shouldn't hurt. What would you classify this as - C1, C2 or an FI ?
Broken ring, sockets getting hot. 20 A accessories on 32A breaker? Fire risk. F1
 

daud09

-
Reaction score
1
An open circuit on any conductor on a ring final circuit should attract a C2. What limitations are preventing you inspecting and testing thus giving an FI code?
The FI code is massively misunderstood and misused, it should be used when a limitation in the inspection prevents you from assessing something and where did to the limitations, you suspect danger or potential danger.
I am going to disagree and advise that you should base the answer on your findings as your initially there to carry out a condition report. If you test a circuit and find there is no conrinuity of CPC and the problem is not starimg you in the face, then you write down FI in order to advise the client as per your findings. If you see a break in cable and again your remit is to report findings then you add C2 to the report. If however, your remit is to report and resolve then you write the code that applies. There is no science and secret behind codes. The issue is people reading too much into a simple task. C1 dangerous, C2 is potentially dangerous, C3 advisory and FI further investigation to determine result.
 

7029 dave

-
Mentor
Esteemed
Arms
Reaction score
2,933
I am going to disagree and advise that you should base the answer on your findings as your initially there to carry out a condition report. If you test a circuit and find there is no conrinuity of CPC and the problem is not starimg you in the face, then you write down FI in order to advise the client as per your findings. If you see a break in cable and again your remit is to report findings then you add C2 to the report. If however, your remit is to report and resolve then you write the code that applies. There is no science and secret behind codes. The issue is people reading too much into a simple task. C1 dangerous, C2 is potentially dangerous, C3 advisory and FI further investigation to determine result.
I disagree, if open circuit has been confirmed on RFC then rectification is the next step not FI surely.?
 

nicebutdim

-
Esteemed
Arms
Reaction score
1,984
I am going to disagree and advise that you should base the answer on your findings as your initially there to carry out a condition report. If you test a circuit and find there is no conrinuity of CPC and the problem is not starimg you in the face, then you write down FI in order to advise the client as per your findings. If you see a break in cable and again your remit is to report findings then you add C2 to the report. If however, your remit is to report and resolve then you write the code that applies. There is no science and secret behind codes. The issue is people reading too much into a simple task. C1 dangerous, C2 is potentially dangerous, C3 advisory and FI further investigation to determine result.

The answer is in the last two letters of the acronym 'EICR'. If you're tasked with repairing anything you find, then any issues you resolved won't be coded - if you find a fault and can't repair it, then you report on the condition of the installation at the time of writing.
 

brianmoooore

-
Esteemed
Arms
Reaction score
2,030
The answer is in the last two letters of the acronym 'EICR'. If you're tasked with repairing anything you find, then any issues you resolved won't be coded - if you find a fault and can't repair it, then you report on the condition of the installation at the time of writing.
Exactly! Repairs are not in the remit of an EICR, although myself and most others will deal with very simple faults to repair as they go. Bit like the MOT test for your car, when the tester sticks on a new wiper blade or changes a brake light lamp to avoid failing the car.
 

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
4,803
my garage issue a fail cert for a faulty lamp
even though i tell them if it needs lamps or brake pads etc, just to do it and send me the bill.

normally i get
fail cert
invoice for number plate lamp etc.
pass cert

i suppose it is the correct way of doing it and also stops the garage from having an unusual pass/fail ratio that might lead them to being checked for irregular practices.

edit, that leads me on to, why dont the part p scams, keep an eye on members that have unusual ratio's of satisfactory vs unsatisfactory eicr's and look closely at the ones who are passing nearly 100% of certificates issued?
 

Reply to EICR - No Line or CPC Continuity on Ring in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

W
Doing an EICR and was looking for some advice, testing the socket circuit, it’s a ring circuit. 3 sockets in the living room area, opened 2 up and they both had one cable at it (great). Opened the 3rd and it had 4, so obviously the other 2 sockets are fed from here. Now I know you are allowed to...
Replies
3
Views
290
littlespark
littlespark
V
Hi, I've just been testing a ring final before installing an outdoor socket and I got an R1 and rn of 0.6, but instead of 1.01 for R2 I got a range of readings from 0.1 to 0.51 and it wouldn't settle down, so I couldn't continue the tests. I know parallel paths could cause a low reading, but...
Replies
6
Views
485
newfutile
newfutile
A
Hi everyone, Looking for honest opinions on C2 ratings on a recent EICR. Terrace house probably built 1930's, rented out. Not sure if this is a standard EICR template but text and C2 ratings for the following: 1. Consumer unit - manual operation of circuit breakers and RCD's to prove...
Replies
14
Views
941
Ann Low
A
Dartlec
Typically the EICR I fitted in this afternoon because I'd hoped it would be fairly simple (new build home, 2007), turned out to be the only recent one that's thrown up a major FI. Downstairs lighting circuit, 1mm T&E, currently on a 6A MCB R1+R2 fine, insulation test L&N -> E an immediate...
Replies
10
Views
438
timhoward
timhoward
FreeBeam
NICEIC Certification Scheme EICR Remedial Works evidence
Hi all, Newbie here and looking for some advice and confirmation. We are planning to rent out our home and have completed EICR through the agents. The EICR came back with a few C2. 240v fan in shower cubicle C2 Socket backbox damaged in lounge C2 Socket backbox damaged in hallway C2 IP of...
Replies
16
Views
615
DPG

Electrical News from Electricians Forums and Friends

E
  • Article
Want to become a qualified electrician? Look carefully at the training courses on offer to avoid wasting time and money, is the advice in a new campaign from electrical industry body The Electrotechnical Skills Partnership (TESP). With thousands of searches each year on terms such as...
Replies
49
Views
6K
Marty92
Dan
  • Article
You can now link your account with social media by going to the following page. https://www.electriciansforums.net/account/connected-accounts/ We had this feature some time ago but I removed it when Facebook was found to be selling the data they collected without informing the users of what...
Replies
0
Views
2K
Dan
Dan
  • Article
There was a dodgy advert, typical clickbait, showing "how to save 90% on your electricity bill" which was not the case and it was actually showing some dangerous wiring tactics. Read the actual threads here:- What should be the code for this - C2 or C3 -...
Replies
37
Views
8K
Jurassic Sparks
Jurassic Sparks
James
  • Article
The Go Plus hot tub is being recalled because you could get electrocuted taking a dip, according to press releases from the Chartered Trading Standards Institute (CTSI). An Amazon spokesperson said: "Safety is a top priority at Amazon. "We require all products offered in our store to comply...
Replies
6
Views
3K
Dave Appleby
D
Dan
  • Article
Posted on behalf of @CKI:C.K-Tools Carl Kammerling International Ltd, also known to as ‘CKI’, are the company behind the C.K Tools brand. Founded in Germany in 1904 and with roots stretching back to 1790, we provide a wide range of hand tools, tool storage, power tool accessories and...
Replies
2
Views
4K
telectrix
telectrix

Search Forum

Top