Hi Guys, Recent EICR carried out at a Church & Hall. Would you code no SPD present at Supply origin & should the Lightning Protection System be connected to the Main Earthing Terminal via another SPD.
 
Should be a type 1 SPD installed - C2
LP should be connected to the MET - C2

Edit: Was the LP system I&T part of the EICR or has this been done seperately?
 
No SPD or interconnect should have received an unsatisfactory LP system report. I'm surprised as a lot of companies will quite happily quote vast sums of money to install an SPD and a bit of green and yellow.
 
Hi, guys & Strima, thought you may like to comment. The following .png from a LPS report. Does this actually say that in other words that no SPD is required ?
 

Attachments

  • 1604057090699.png
    69.8 KB · Views: 37
No, that statement clearly indicates that a lightning strike would not be discharged safely as the protection system is not installed properly, and extensive damage would likely be the result.
 
Hi Guys, Recent EICR carried out at a Church & Hall. Would you code no SPD present at Supply origin & should the Lightning Protection System be connected to the Main Earthing Terminal via another SPD.
Itas all down to the survey you carry out on the installation, the book has a map of areas prone to strikes, and the equipment that may need protection in the propery , for example a house with the THTC set up with sometimes 3 boards why would you want to protect storage heaters, and convectors, I only consider the house circuits maybe the boiler if its got electronics for example there is no set rule for all properties, Lightning conductors I would not be encourging lightning to find a path into the home via the MET
 
OP. Recent EICR carried out at a Church & Hall. Would you code no SPD present at Supply origin & should the Lightning Protection System be connected to the Main Earthing Terminal via another SPD.
New Post. I see a Type 1 SPD was suggested at the origin of the supply.
As I understand Spd protection a Type 1 SPD is to prevent Flashover from a direct strike, causing break down of the insulation. Then a Type 2 is to prevent transient voltages to the rest of the installations sensitive equipment. The installation origin at the Church Hall is quite a distance from the LPS conductor & is not directly connected to the MET at present. I am limited for space for a standalone Type 1, I don't think the DNO would appreciate it on their External meter Box Board. As there is hardly any sensitive equipment other than a CD player for the Church service & an Office PC, I am inclined to install just a Type 2 in the main Consumer Unit. Do I need the Type 1 at the origin plus a Type 2 in the Consumer unit & what about the other 2 sub mains C/units? Obviously, there is a substantial price difference between the 2 devices. not much on the collection plate these days. Thanks guys for your input!
 

Reply to EICR no SPD &LPS Enquiry in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, just carried out an EICR on a rented property that has mains smoke detectors, there is no SPD fitted and as I understand any safety...
Replies
1
Views
5K
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
468
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Following the tragic tale from @telectrix about lightning damage to phones and modem leading to a serious loss of beer money I decided to take a...
Replies
0
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock