so it's bordering between a C! and a C2, i
 
Sounds like a TT system with a dodgy earthing terminal.
There are other likely culprits along the way. Earth loop testing through a RCBO?
I would first check the earthing system.
Earthing from a fortuitous routing or some pretty lousy conections or there really is no earth in the socket circuit or all of them.
 
I'd have to agree with Ian on this. The circuit does not meet ADS due to very high impedance, however it would require a fault to present an immediate danger. C2 for me.
 
C2.
 

Reply to Eicr,oh the joys of sparkies... in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock