i can see why he has done that!! as MOST showers stipulate protection by RCD...

end of the day the PIR is based on what you deem safe/unsafe.... nobodys decisions or suggestions should influence YOUR decision
 
Well if there is no supp bonding and that was required to limit the different potentials of exposed metalwork then this is potentially dangerous so I would code it as a C2 unless there was an RCD fitted to all circuits in the bathroom and main bonding was present.
What you have to watch for here IMO is that while the electrical installation (fuseboard etc) maybe as they were when installed, most often the bathroom has had a make over -during which the supp bonding was not re-installed. In this case the person ordering the work has a choice re-instigate the supp bonding or upgrade board (and bonding).

From 4. Periodic inspection of existing domestic and similar installations : Electrical Safety CouncilQ4.4
What Classification Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?
[FONT=&amp]Classification Code C2. Where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test (< 0.05 ?)[/FONT]
 
Not according to the ESC Electrical Safety Council
From 4. Periodic inspection of existing domestic and similar installations : Electrical Safety CouncilQ4.4
What Classification Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?
[FONT=&amp]Classification Code C2. Where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test (< 0.05 ?)[/FONT]
 
Not according to the ESC Electrical Safety Council
From 4. Periodic inspection of existing domestic and similar installations : Electrical Safety CouncilQ4.4
What Classification Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?
Classification Code C2. Where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test (< 0.05 ?)

The OP didn't mention supplementary bonding!!
 
But he is talking about Regulation 701.415.2 and this is conditional on whether the install meets the regs in force at the time - so it is pertinent that the Supp boning should be met - if it is then it is a C3 possibly if not it is certainly a C2 according to the advice from the esc
 
When you do an inspection the reason for the inspection and the type of use of the building and the users has to be taken in to account. Landlords have a duty of care under law towards their tenants.
The ESC is calling on landlords to ensure that there is adequate RCD protection in all of their properties as fewer than half of UK households (49%) have adequate RCD protection and the number drops to just 30% for private tenants. A Residual Current Device (RCD) is a life-saving device that protects against dangerous electric shock and reduces the risk of electrical fires. Plug-in RCDs should be used if there is no RCD in the fusebox.

Press Releases News : Electrical Safety Council

Extract

By law, landlords must ensure electrical installations and wiring are maintained in a safe condition throughout the tenancy . And tenants should feel obliged to flag electrical problems as soon as they appear, as well as maintain any electrical items they bring into the house. The consequences for not understanding obligations can be serious. If a landlord is found to be negligent over electrical safety it can lead to prosecution, with a fine of up to £5,000 on each count or imprisonment. This may come as a shock to the 38% of landlords who don’t believe there are any penalties for failing to maintain safety.

 
Its code 3 regardless of bathroom bonding or not.
From the ESC EICR guidlines giving examples of C3's ;

"Absence of RCD protection in a location containing a bath or shower where satisfactory suplementary bonding is present "

Its all there , clear as crystal but nobody could be arsed looking the facts up properly.
Apart from me ;-)
 

Reply to Eicr question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Replies
10
Views
776
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
692
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
859

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock