can anyone point me to a few Reg Numbers.

16mm Earthing conductor has been cut and twisted together? needs to be continuous.



MAIN KIOSK, MAINS & GENERATOR SECTION, 16MM Cables from main isolator to 63A fuses are showing signs of burning.(Reg ?????
 
can anyone point me to a few Reg Numbers.

16mm Earthing conductor has been cut and twisted together? needs to be continuous.




MAIN KIOSK, MAINS & GENERATOR SECTION, 16MM Cables from main isolator to 63A fuses are showing signs of burning.(Reg ?????[http://www.electriciansforums.co.uk...electrical-forum/110074-eicr-regs.html/QUOTE]

Sorry mate couldn't resist

http://www.electriciansforums.co.uk/electrical-forum-general-electrical-forum/110074-eicr-regs.html


Sorry I'll try again

https://www.youtube.com/watch?v=87EwAzFfO2M
 
As far as I can find in the regs, the main earth cable does not have to be continuous, but in your situation, it should be joined securely. It is only bonding cable that bonds more than one item that are required to be continuous.
 
As far as I can find in the regs, the main earth cable does not have to be continuous, but in your situation, it should be joined securely. It is only bonding cable that bonds more than one item that are required to be continuous.

Where in the regs did you find all of that?
 
As far as I can find in the regs, the main earth cable does not have to be continuous, but in your situation, it should be joined securely. It is only bonding cable that bonds more than one item that are required to be continuous.

not necessarily. although it's good practice to ensure that the removal of one bond ( usually by a wet-pants ) does not compromise the integrity of others. )
 
Where in the regs did you find all of that?

I looked through the online version of “Guidance Note 8: Earthing & Bonding” searching for “Continuous” and the only reference in the context of a cable being continuous is in bonding multiple items (Guidance Note 8: Chapter 5.2 says “However, it is permitted to connect them collectively or in groups where the main protective bonding conductor is looped from one extraneous-conductive-part to another. Where bonding is undertaken in this way, the bonding conductor should remain unbroken at intermediate points, as shown in Figure 5.5, thus maintaining continuity to other extraneous-conductive-parts should one be disconnected for whatever reason.”).
Then I looked through the first 4 chapters describing earthing and there is no mention of the cable between the MET and consumer unit being unbroken or continuous.
It is common sense and good practice to make the cable continuous, but does not appear to be part of any regulation I can find, therefore it is hard to give it an EICR code as long as the join is safe, supported and not going to come apart.

I hope I have this correct.
 
Last edited:
Most times that I have seen them removed they are still on the clamp. we must have plumbers with no cutters up here .
One of the favourite tricks up here is under the floorboards. No prizes for guessing what it is.
 

Reply to EICR Regs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
758
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock