graham123

Main switch 160a bs88fuses, 35mm tails feeding busbar chamber with switch fuses ontop feeding distribution boards. A c2 has been given to undersized main tails. I thought that because the tails are only about 400mm long from switch into busbar that it was ok? Thoughts?
 
according to table 6D1 ( red osg) ccc if tails are ref. method F ,and spaced, the ccc of 35mm is 161A - 181A, so can't see a problem as In<Iz.
 
The main switch is bolted under the busbar so reference method is just enclosed. 110a but I'm sure I have come across this before were it's acceptable as it's less than 3 meters
 
according to table 6D1 ( red osg) ccc if tails are ref. method F ,and spaced, the ccc of 35mm is 161A - 181A, so can't see a problem as In<Iz.
Think the OP may be worried about the lack of protection of the tails from the BB to the SF the 3mtr ruling that concerns most people, they are not the same size as the cables feeding the BB Chamber, forgot to add that bit hence the edit
 
So down stream its a 100 amp fuse with a 160 amp fuse upstream? How can the tails be undersized?

Also how can the person who did the EICR be deemed competant if thats the case?
 

Reply to Eicr remedials in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
789
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
942
Evening, I've been asked to install a supply to a sprinkler system in a new installation that must be separate to the building electrical...
Replies
2
Views
554
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
803
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock